[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Zone Equipment List problems




Thank you so much for your clear explanation!

Eduard

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@...> wrote:
>
> This model has an air loop VAV with reheat and radiant hydronic
cooling serving 
> the same zones, and both system are autosized.
> 
> 1.  EnergyPlus autosizing does not understand if there is more than
one system 
> serving the same zone.  It will size both system to meet the full
cooling load.
> 
> 2.  In the input file, the VAV terminal unit is priority 1 for
cooling, and the 
> radiant hydronic is priority 2.  So, if the VAV unit can meet the
thermostat 
> setpoint (which it will since it has been autosized), then there is
no load 
> remaining for the radiant cooling to serve.
> 
> 3.  So, revsersing the cooling priorities in zone 1N results in the
radiant 
> hydronic system showing flow, and the VAV box sitting a min flow.
> 
> 4.  However, in milder weather, the zone will probably overcool due
to the min 
> flow from the VAV box and the reheat will come on, which is not what
you want.  
> So, you will probably need to hand size one of both systems in order
to share 
> the load.  And you need to decide which system should be priority 1
and 2.
> 
> Mike
> 
> 
> On 6 Sep 2007 at 21:48, eduardcubi wrote:
> 
> > Hi all,
> > 
> > I have some problems when including radiant cooling systems in the
> > zone equipment list. 
> > It seems that when I assign the systems to their respective zones
> > (e.g. "z1N Radiant Ceiling" under "z1N Equipment") these don't work
> > (i.e. there is no temperature gain from the inlet to the outlet, and
> > the flow rate is 0). However, if I "do a mess" with the assignations,
> > it "works" (e.g.  "z1E Radiant Ceiling" under "z1N Equipment").
> > 
> > I have checked everything I think that may be relevant, but I couldn't
> > find the source of the error.
> > 
> > Could you help me?
> > 
> > Thanks a lot,
> > 
> > Eduard
> > 
> > P.S. I have updated the file: "newtest.idf"
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the
appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf
under the
> > Documentation link and press the "search" button.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@...
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/