[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Purchased Air Heating/Cooling Loads



If you are looking for sensible heating and cooling loads, then these will be 
equivalent:

  Purchased Air Heating Rate[W]
  Zone/Sys Sensible Heating Rate[W]

  Purchased Air Sensible Cooling Rate[W]
  Zone/Sys Sensible Cooling Rate[W]

Purchased air also computes the latent load required to provide the user-
specified humidity ratio.  This may or may not be useful depending on the 
particular application, because Purchased Air does not control the zone to a 
specific humidity level.  Purchased Air Total Cooling Rate[W] includes this 
latent load.

Mike


On 23 Oct 2007 at 15:12, brandao_nuno wrote:

> Dear All,
> 
> I´m a recent EnergyPlus user and began simulating a simple 3Zone case
> study, with no HVAC system. The objective is to determine the Heating
> and Cooling loads of the building. It seems to me that PurchasedAir is
> the best solution to determine loads without defining HVAC system. In
> the Reports/Report Variable object, there are two similar variables
> which we obtain(I think) we obtain equal results. The variables are:
> "Purchased Air Heating Rate" or "Purchased Air Total Cooling Rate" and
> "Zone/Sys Sensible Cooling Rate" or "Zone Sys Sensible Heating Rate".
> What's the main diference between these two report  variables? Is
> there any other variables which i should be aware of, that can give
> more precise results?
> 
> Thank´s
> Kind Regards
> Nuno Brandão
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/