[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] solar powered intermittent absorption refrigeration unit



Dear all,

I would like to model a solar powered intermittent absorption 
refrigeration unit to justify the feasibility of the unit on solar 
power.Is there any way so that I can connect the absorption 
refrigeration unit directly with the solar collectors in EP? 

Warmest regards,
Ashfaque

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jun Calixihan" 
<jcalixihan@...> wrote:
>
> Hi!
> 
>  
> 
> Need help identifying source of error in my model for absorption 
chiller.
> Below is the error.  I tried editing the condenser pump, chiller 
parameters,
> equipment sizes, loop temperatures, etc. but can't seem to arrive 
at the
> source of error.  I uploaded the idf file named
> AbsorptionChillerModified.idf
> 
>  
> 
> Thank you in advance!
> 
>  
> 
> Best Regards,
> 
> Jun
> 
>  
> 
>  
> 
> ** Warning ** SizeCondDemandSide: Calculated Plant Sizing Design 
Volume Flow
> Rate=[0.00] is too small. Set to 0.0
> 
>    **   ~~~   ** ..occurs for Condenser Loop=CHILLED WATER LOOP 
CONDENSER
> WATER LOOP
> 
>    ** Warning ** SizeCondSupplySide: Calculated Plant Sizing Design 
Volume
> Flow Rate=[0.00] is too small. Set to 0.0
> 
>    **   ~~~   ** ..occurs for Condenser Loop=CHILLED WATER LOOP 
CONDENSER
> WATER LOOP
> 
>    ** Warning ** SizePump: Calculated Pump Nominal Volume Flow Rate=
[0.00]
> is too small. Set to 0.0
> 
>    **   ~~~   ** ..occurs for Pump=CHILLED WATER LOOP CNDW SUPPLY 
PUMP
> 
>    ** Warning ** Check input. Pump nominal power or motor 
efficiency is set
> to 0, for pump=CHILLED WATER LOOP CNDW SUPPLY PUMP
> 
>    ** Warning ** Check input. Pump nominal volumetric flow rate is 
set or
> calculated = 0, for pump=CHILLED WATER LOOP CNDW SUPPLY PUMP
> 
>    ** Severe  ** CalcBLASTAbsorberModel: Condenser flow = 0, for
> Absorber=CHILLER
> 
>    **  Fatal  ** Program Terminates due to previous error condition.
> 
>    ...Summary of Errors that led to program termination:
> 
>    ..... Reference severe error count=1
> 
>    ..... Last severe error=CalcBLASTAbsorberModel: Condenser flow = 
0, for
> Absorber=CHILLER
> 
>    ************* Fatal error -- final processing.  More error 
messages may
> appear.
> 
>    ************* Testing Individual Branch Integrity
> 
>    ************* All Branches passed integrity testing
> 
>    ************* Testing Individual Supply Air Path Integrity
> 
>    ************* All Supply Air Paths passed integrity testing
> 
>    ************* Testing Individual Return Air Path Integrity
> 
>    ************* All Return Air Paths passed integrity testing
> 
>    ************* No node connection errors were found.
> 
>    ************* EnergyPlus Terminated--Fatal Error Detected. 8 
Warning; 1
> Severe Errors; Elapsed Time=00hr 00min  2.91sec
> 
>  
> 
>  
> 
>  
> 
> 
> 
> [Non-text portions of this message have been removed]
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/