Re: [EnergyPlus_Support] Effects of Zone and System Sizing?



Your approach of replacing "autosize" with hard values either in the Compact 
HVAC objects or in the expidf file objects is the correct way to force the 
system size to stay the same across alternatives.  Theoretically, both 
approaches should have produced similar results.  I would need to see the input 
files in order to explain why they differed.  

Regarding the result where changing thermostat setpoint does not alter energy 
consumption . . . This would lead me to think that the zone temperatures are 
not well-controleed for either setpoint, that the system is maxed out on 
capacity in both cases.  But that is just a guess.

Mike


On 10 Dec 2007 at 16:29, eric.mcmaster wrote:

> Hello,
> 
> I have been working with EnergyPlus Simulation files attempting to 
> assess the impact of various Energy Efficiency Retrofits on the 
> energy consumption of a specific building.  I am developing 
> EnergyPlus files using Compact HVAC Description and my question 
> relates to the factors within the building that are being auto sized 
> within EnergyPlus due to this fact. As I wish to assess the effects 
> of changing building components on a building with static mechanical 
> systems I was wondering if you could explain how to ensure that the 
> mechanical systems are remaining constant and now being re-sized 
> within EnergyPlus after each incremental change. 
> 
> I have so far attempted two separate methods for achieving a static 
> building system model.  First I ran a base level EnergyPlus file; 
> when the simulation was completed I extracted the information 
> available within the ".eio" output file which listed the values 
> determined for in the auto sizing of components.  I then replaced 
> the "auto size" parameters with the corresponding input parameters in 
> first the Compact HVAC Objects and then in the expanded .idf objects. 
> Both methods produce different results for pump and fan loads when 
> simulating for Energy efficiency retrofits (EERs). Specifically, when 
> the expanded .idf file was defined using all of the original 
> component sizing information EERs such as a change in cooling set 
> point temperature now have no effect on consumption.
> 
> What would be the best way to most accurately define a building 
> within EnergyPlus which possesses static building system information?
> 
> Thank you
> Eric
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/