[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Design Volume Flow Rate



INFILTRATION is normally used to represent airflow through cracks in the 
building envelope and airflow which occurs from occasional opening of doors.  
The air which enter the house when all windows and doors are open would be 
better modeled using VENTILATION, or in more details using AirflowNetwork:*.

Mike


On 12 Dec 2007 at 14:39, tasos.ioannou wrote:

> Dear Forum,
> I am modeling a Mediteranean house, located in Athens, Greece. I would 
> like to ask you how can I find values for Design Volume Flow Rates. 
> This is a field for the INFILTRATION object. The Input/Output reference 
> document says that this is the maximum infiltration value expected in 
> design conditions. Does this mean the amount of air that enters the 
> house when all windows and doors are open? And if you please have any 
> idea for standar values, or how I could calculate this value for a 
> specific place, in my case Athens, this would be very helpfull. I hope 
> for an answer, thank you in advance.
> 
> Best regards 
> 
> Tasos Ioannou
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/