[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] errors about zone splitter



By editing the Energy+.idd file, the zone splitter and zone mixer objects can 
be extended beyond 50 zones.  But the bigger issue is a simulation in which one 
air handling unit serves 40 stories.  You will have a better model if you use 
mutiple air handlers to serve such a large building.

Mike


On 5 Jan 2008 at 18:30, Griffith, Brent wrote:

> Zone splitters are limited to 50.  If you have more than 50 zones, you'll need
> multiple air systems.  Another option is to use multipliers and model only a few
> floors.  
> 
> 
> 
> ________________________________
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of beyangj Sent: Saturday,
> January 05, 2008 9:04 AM To: EnergyPlus_Support@xxxxxxxxxxxxxxx Subject:
> [EnergyPlus_Support] errors about zone splitter
> 
> 
> 
> Dear all,
> 
> When I opened the IDF file exported from a DesignBuilder model, there 
> were many IDF Paring Error messages popup one by one. The message is 
> ¡°Too many fields for objects: ZONE SPLITTER¡±. 
> 
> There are 6 zones every floor, and there are 40 stories in my 
> DesignBuilder model. When there are less than 10 stories in the model, 
> there is no error message poping up when I opened the IDF file 
> exported from a DesignBuilder model. When there are more than 10 
> stories in my DesignBuilder model, the Error messages mentioned above 
> popup again when I open the IDF file exported from it. There is no 
> error when I run my model in DesignBuilder. Could you help me why this 
> happened? Thanks a lot in advance.
> 
> Young
> 
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/