[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Water Use Equipment as mister simulation



hi All
Well I have created the mister cooling simulation using the 
recommendation that I got with the Water Use Equipment. I have got 
everything working, and been able to observe the "latent heat rate to 
zone" variable and "zone relative humidity" behave fairly well. What I 
haven't been able to do is actually change the mean air temperature of 
the zone which is what I am trying to do. 

If I change the flow rate of the water use equipment from 0 to a high 
number that pushes the rel humidity through the roof it doesn't change 
the mean air temperature. 

If anyone could tell me what I am doing wrong it would be great!
cheers
Danny



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/