Thanks Richard. I donot quite understand when you said both chillers 
will operate at the same evaporator volumeric flowrate. Can I bypass 
some of the chilled water flow around the small chiller? In this 
way, the big chiller can have a higher flow and the small chiller 
has a lower flow. 

Thanks again,
Chaoqin

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad 
<RRaustad@...> wrote:
>
> This should work in E+. You would need to use constant flow 
chillers and 
> the chillers should not be auto-sized (or at least the smaller 
one). The 
> only problem I see is that you can not have a significant 
difference in 
> the capacities of the series chillers. The reason is that both 
chillers 
> will operate at the same evaporator volumetric flow rate (and the 
> performance curves should account for off-design flow rates). 
There is 
> an upper (and lower) limit to the water velocities through a 
chiller's 
> heat exchanger. Above the upper limit, erosion of heat exchanger 
will be 
> excessive (and so will the pressure drop). Below the lower limit 
there 
> is a chance of freezing the heat exchanger or reducing oil 
transport 
> through the refrigeration system. Of course this will not hurt the 
> simulation, but you want to be as close to reality as possible. 
And if 
> you actually built a chiller with an over-sized heat exchanger, 
you 
> would not have this problem. Check with manufacturers for 
appropriate 
> ranges of water flow rates through the evaporators for your type 
of 
> chiller. The same holds true for the condenser heat exchangers, 
but you 
> could pipe the condensers in parallel.
> 
> zhaicq98 wrote:
> >
> > I have a big and a small water cooled vapor compression chiller 
in the
> > system. They are configured in series, but the chilled water 
flowrate 
> > of the
> > big chiller is much greater than the small one. The small 
chiller is 
> > used to
> > pre-cool a portion of the chilled water return to the big 
chiller.
> >
> > I wonder if EnergyPlus is able to handle this system. Thanks for 
your
> > help.
> >
> > -Chaoqin
> >
> >  
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/