Re: [EnergyPlus_Support] horizontal openings



ROTRAT:

Your understanding is correct. The existing AirflowNetwork model is unable 
to calculate air recirculation across a large horizontal openings. One way 
flow will be obtained across an opening due to constant height for a large 
horizontal opening. Adding more openings does not help, because the airflow 
across an opening is calculated based on the pressure difference between two 
zones. We have a plan to add this capability. Do you have any good 
suggestions?

By the way, I found you input interior walls twice in the network input. 
Here is a paragraph extracted from the Input Output Reference on page 621:

Note: It is possible to define an interzone surface twice in EnergyPlus, 
once in each of the zones that the
surface separates. Previously this was a requirement of EnergyPlus (prior to 
version 2.0), but now it is
optional and the user also has the option of only defining the surface once 
(EnergyPlus defines the second
surface automatically within the program). For each interzone surface, use 
only one (of possible two)
interzone surface names in the AirflowNetwork:Multizone:Surface object for 
"Name of Associated Heat
Transfer Surface." Do not enter two AirflowNetwork:Multizone:Surface objects 
corresponding to the two
possible interzone names. This would cause the air flow through the surface 
to be counted twice.

Please let me know if you have more questions.

Lixing

----- Original Message ----- 
From: "ROTRAT Leelatanon" <copper_one_oxide728@xxxxxxxxx>
To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Sunday, February 03, 2008 12:34 PM
Subject: [EnergyPlus_Support] horizontal openings


> My objective is to simulate the building to find out how temperature will 
> reach if i put little amount of cooling load in the building, but only 
> natural ventilation is needed
>
> I am simulating the buiding with some horizontal openings which I defined 
> them in subsurface. As i read the documentation about AirflowNetwork, it 
> lead me to example AirflowNetwork3zVentAutoWPC. After input my own data i 
> found that horizontal openings cannot be well used in 
> AirflowNetwork:Multizone:Surface.
>
>  Is there any other possible way to fix this, I need to study the amount 
> of air that circulate through these horizontal openings
>
>  I have attached my .idf for your comment and suggestion
>
>  thank you in advanced
>
>
> ---------------------------------
> Looking for last minute shopping deals?  Find them fast with Yahoo! 
> Search.
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate 
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the 
> Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
> 



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/