[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Add a simple thermal load to a simulation?



Hi Ana

You can use the "Non-Zone equipment->Plant Load profile". There you can
insert a load schedule and connect this virtual load to the chilled water
loop as a "branch".

Hope this helps

E. Sá

2008/2/7, anarui.oliveira <anarui.oliveira@xxxxxxxxx>:
>
>   Hello.
>
> Is there a simple way to introduce a "virtual" thermal load on a
> simulation, so that, when simulating only a part of a set of buildings,
> which are all served by the same chiller or heat pump, the chiller/heat
> pump is asked to respond to the full load it must meet in the actual
> situation (and thus operate at the correct partial load and efficiency)?
>
> Thanks,
> Ana Rui.
>
>  
>


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/