[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Energy storage into a wall



Thank you for answer!

The output value of EnergyPlus:
Surface Ext Rad to Air Coeff[W/m2-K](Hourly)
Surface Ext Rad to Sky Coeff[W/m2-K](Hourly)
Surface Ext Rad to Ground Coeff[W/m2-K](Hourly)

are zero, is it correct?
The Energy Plus doesn't calculate the coefficient for radiation  
exchange with the air mass, exchange with the sky, exchange with the  
ground. Is it true?

Thanks for collaboration!
Thanks a lot for any help!

Michela





Citando "Michael J. Witte" <mjwitte@xxxxxxxx>:

> Have you tried a steady-state design-day case to make sure that everything
> balances as expected?  Perhaps there is a missing term in your formulation of
> the exterior surface heat balance.
>
> Mike
>
>
> On 8 Feb 2008 at 10:37, Michela wrote:
>
>> Hello!
>> I?m trying to evaluate the role of thermal
>> inertia of an exterior wall of a very simple
>> building in purchased air simulation. The idea is
>> to calculate the energy stored into and released by the wall, say DE.
>>
>> For this I use ?conduction into the wall, qko?
>> and ?conduction from outside, qki?, like defined
>> in the manual Engineering Reference page 35 and 48 respectively.
>>
>> I calculate qko by summing the energy flows at
>> the exterior surface as it is described on page
>> 35 of the Engineering Reference:
>> qasol + qLWR + qconv ? qko = 0
>>
>> Instead I obtain qki from the Energy Plus
>> outputs: ?Opaque Surface Inside Face Conduction
>> Gain[W](Hourly)? and ?Opaque Surface Inside Face Conduction   
>> Loss[W](Hourly)?.
>>
>> I assume the following sign convention:
>> qko >0 if the flow enters into the wall
>> qki >0 if the flow enters into the internal zone.
>>
>> Then the internal energy variation of the wall in a time step is   
>> calculated as:
>> DE = (qko ? qki) Dt
>>
>> It should be that if DE < 0 the wall is loosing
>> energy, while if DE > 0 the wall is storing energy.
>> Then I expected to find that DE changes its sign
>> during the day, showing the heat storage and
>> realease. But on the contrary during the summer
>> period I observed that the wall always has a
>> negative energy variation. The wall has more loss
>> then gain. But, looking at the outside and inside
>> surface temperatures of the wall, they are not constantly decreasing.
>>
>> How do you feel with this result? Did anybody
>> ever try a similar analysis? May you suggest any
>> other way to study the energy storage into the wall?
>>
>> Thanks a lot for any help!
>>
>> Michela
>>
>>
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> Attachments are not allowed -- please post any files to the   
>> appropriate folder
>> in the Files area of the Support Web Site.
>>
>> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
>> Documentation link and press the "search" button.
>>
>> Yahoo! Groups Links
>>
>>
>>
>>
>>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
>






The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/