My guess is the zone origin for this zone (LEVEL1) has a y-value of 2.25.  If 
you are working in world coordinates, then set the zone origin to 0,0,0.  If it 
is not 0,0,0 it will shift the daylighting reference points and the daylighting 
map coordinates.  (Note that this behavior will be optional in the next 
release.)

Mike


On 14 Feb 2008 at 6:33, ooikoonbeng2004 wrote:

> Dear all, 
> 
> Why is it that the Y ref point = 12.25 when i set the max to 10.00? 
> The two warnings in the .err file are as follows: 
> 
> Program Version,EnergyPlus 2.1.0.023, 14/02/2008 5:17 PM,IDD_Version 
> 2.1.0.023
>    ** Warning ** World Coordinate System selected.  Any non-zero 
> Building/Zone North Axes or non-zero Zone Origins are ignored.
>    **   ~~~   ** These will be used in Daylighting:Detailed 
> calculations but not in normal geometry inputs.
>    ** Warning ** SetUpDaylightCoords: Reference Map point Y Value 
> outside Zone Min/Max Y, Zone=LEVEL1
>    **   ~~~   ** ...Y Reference Point= 12.25, Zone Minimum Y= 0.00, 
> Zone Maximum Y= 10.00
> 
> The Y coordinates of the two reference points in the Daylighting 
> Detail object are 3 and 6.
> 
> regards,
> ooi 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/