[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Radiant Ceiling Heating??



Hi Tasos;

If you don't put another Surface:HeatTransfer object on "top" of the
"bottom" one with the CONSTRUCTION WITH INTERNAL SOURCE, and instead specify
the "bottom" Surface:HeatTransfer object as adiabatic, you won't get any
radiant heat transfer from the top side of the panel to the ceiling of the
zone. That's why I used the two surface approach.

Josh


On Thu, Apr 3, 2008 at 10:50 AM, Tasos Ioannou <tasos.ioannou@xxxxxxxxx>
wrote:

>   Hi Josh,
>
> Thank you for the reply and your information. Though I would like to ask
> you why did you make two surface heat transfer objects and not only one? Why
> not making this radiant panel only as a construction with internal source?
> You made another surface that you put on top of the construction with
> internal source. Was that necessary? Thank you again for the valuable reply
> and hope to hearing from you soon.
>
> Best ragards
>
> Tasos Ioannou
>
> Josh K <jeemang@xxxxxxxxx <jeemang%40gmail.com>> wrote:
> Hi Tasos;
>
> I had to model something similar to this, and I ended up creating a couple
> of Surface:HeatTransfer objects, with each one specified as the surface in
> the other's "OutsideFaceEnvironment object" field. I created one surface
> to
> represent the "bottom" of the panel and one to represent the "top," with
> each surface's normal facing "into" the panel. For the "bottom" surface I
> used a CONSTRUCTION WITH INTERNAL SOURCE and for the top surface just a
> regular CONSTRUCTION with the same elements as the bottom surface but in
> opposite order (just like you would do with adjacent wall surfaces). One
> last thing: the panels I'm modeling have insulation on the "top" side (ie,
> the side opposite the room they're heating), and before I knew this I
> tried
> to model the panels without an insulation layer on top. I got some errors
> and weird results that only stopped when I added at least one non-metal
> MATERIAL:REGULAR to either of the CONSTRUCTION objects.
>
> I seemed to get pretty good results with this approach. If you have the
> DisplayExtraWarnings option selected in the DIAGNOSTICS object you'll get
> some "severe error" warnings about having interzone surfaces in the same
> zone, but they don't seem to affect the running of the simulation.
>
> Josh
>
> On Wed, Apr 2, 2008 at 8:07 AM, tasos.ioannou <tasos.ioannou@xxxxxxxxx<tasos.ioannou%40yahoo.com>
> >
> wrote:
>
> > Dear Forum,
> >
> > We are modeling a building that is using a Hydronic Radiant System
> > with embedded hydronic tubes inside the walls. In order to model this
> > system we will use the Low Temp Radiant System: Hydronic object that
> > EnergyPlus is providing. At the same time the building is also using
> > another system that is called Radiant Ceiling Heatingwhich is a
> > development of the traditional Hydronic Radiant Ceiling Heating. The
> > radiant element is enclosed in a steel casing 600x600 mm that will be
> > hanging from the ceiling of each zone/office above each desk. Does
> > anyone know how can we model this second system? Which object is the
> > best option for such an independent, enclosed, hanging Radiant Unit?
> > Thank you in advance...
> >
> > Regards
> >
> > Tasos
> >
> >
> >
>
> --
> Josh Kjenner, EIT, LEED AP
> Manasc Isaac Architects Ltd.
> 10225 100 Avenue :: Edmonton, AB T5J 0A1
> 780.429.3977
>
> [Non-text portions of this message have been removed]
>
> ---------------------------------
> You rock. That's why Blockbuster's offering you one month of Blockbuster
> Total Access, No Cost.
>
> [Non-text portions of this message have been removed]
>
>  
>



-- 
Josh Kjenner, EIT, LEED AP
Manasc Isaac Architects Ltd.
10225 100 Avenue :: Edmonton, AB T5J 0A1
780.429.3977


[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/