[EnergyPlus_Support] Re: Heat Recovery Option for Compact HVAC: Unitary appears to not work



A bit more info about the heat recovery problem. Using a shoe-box model and compact HVAC, I ran several outside air percentages. Results are below.

RUN-1: 0% outside air = 5,126 therms/year

RUN-2: 30% outside air = 21,635 therms/year

RUN-3: 100% outside air = 64,344 therms/year

RUN-4: 100% outside air with 70% efficient heat recovery=64,344 therms/year . [I was expecting an answer of about 21,000 therms.]

The heat recovery mechanism had negligible effect. The Compact HVAC part of the model is shown below for Heat Recovery. Am I missing something, or have I come across a bug in Energy Plus?

Jim McNally
-----------------------------------------------------------------------------

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "jim_mcnally" <jim_mcnally@...> wrote:
>
> Hi,
> I have been trying to simulate a unitary HVAC device with a heat
> recovery module. I am using the Compact:Unitary equipment simulation.
> The heat recovery option does not materially change the energy use
> results.
> A one zone building with one rooftop unit is my quick running test
> model. The compact unitary part is given below.
>
> Am I missing something?
> Regards,
> Jim McNally
>
>
> ****** COMPACT UNITARY PART OF EP MODEL ******
> !- =========== ALL OBJECTS IN CLASS: COMPACT HVAC:THERMOSTAT
> ===========
>
> COMPACT HVAC:THERMOSTAT,
> TSTAT-ADM_1FL,                           !- Thermostat Name
> ,                                                               !- Thermostat Heating Setpoint Schedule
> 22.2222228109101,                      !- Thermostat Constant Heating Setpoint
>

> ,                                                                !- Thermostat Cooling Setpoint Schedule
> 22.7777783811828;                      !- Thermostat Constant Cooling Setpoint
> >
> COMPACT HVAC:THERMOSTAT,
> TSTAT-CENTER,                                !- Thermostat Name
> ofc_HTG-Temp_SCHED,                !- Thermostat Heating Setpoint Schedule
> ,                                                                !- Thermostat Constant Heating Setpoint
>
> ofc_CLG-Temp_SCHED,                 !- Thermostat Cooling Setpoint Schedule
> ;                                                                !- Thermostat Constant Cooling Setpoint
>
>
> COMPACT HVAC:THERMOSTAT,
> TSTAT-RESIDENT,                            !- Thermostat Name
> Resident_HTG-Temp_SCHED,     !- Thermostat Heating Setpoint Schedule
> ,                                                                 !- Thermostat Constant Heating Setpoint
> {C}
> RESIDENT_CLG-Temp_SCHED,  !- Thermostat Cooling Setpoint Schedule
> ;                __._,_.___

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___