I don?t know TAS and IES but is sounds like they are old fashioned models whose ?convection coefficient? actually combines convection and thermal radiation into a single coefficient. That is what E+?s ?simple? model does.
Combining convection and radiation into a single coefficient is a simplification that many older/simpler programs make to model heat flows. But it is a poor approach when calculating surface temperatures.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of hvacgeshen516
Sent: Tuesday, June 02, 2009 12:57 AMSubject: [EnergyPlus_Support] About exterior surface convection coefficient algorithms in EP
If the algorithms except simple are chosen, the wind-driven convection coefficient will be much smaller than algorithms implemented by other software like TAS or IES.
Is there any comments on this?
Thanks and Regards
Xiangjing =)