RE: [EnergyPlus_Support] warnings





BANDAR SERI BEGAWAN  is very near Kuala Belait.  There will be a slight solar  time shift in the results, which would not be significant.

 

 

For the ground temperature, you should add the following in the IDF.



!- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:BUILDINGSURFACE ===========

Site:GroundTemperature:BuildingSurface,
   20.0, 20.0, 19.0, 19.0, 18.0, 18.0,  18.0, 18.0, 19.0, 19.0, 20.0, 20.0;

 

 


If you have a large building, you may increase these to 22.0°C.

 

If the building is naturally ventilated, they  may be increased to 24.0°C. 

 


    Notice that the value is higher for January and December.  The minimum is around June. 
 
    This is because the JUne month is Winter in Australia, and the ocean current surrouonding KUALA BELAIT iz from the South.  The trend of the values are listed in the .stat file for BANDAR SERI BEGAWAN weather file.
 
   I first noticed this from working with Mr. Ooi at UNIMAS, Kuching.
 Dr. Li  

 


To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: veronikashabunko@xxxxxxxxx
Date: Thu, 26 Apr 2012 03:51:57 +0000
Subject: [EnergyPlus_Support] warnings

 
Hi everyone,

Thank you very much for the help with previous issue SketchUp and E+. All suggestions were very helpful and highly appreciated!

I am doing simulation in tropical region, but weather file is only for capital city and houses located in urban area.Therefore Eplus give me following warning:

** Warning ** Weather file location will be used rather than entered Location object.
** ~~~ ** ..Location object=KUALA BELAIT
** ~~~ ** ..Weather File Location=BANDAR SERI BEGAWAN - BRN IWEC Data WMO#=963150
** ~~~ ** ..due to location differences, Latitude difference=[0.36] degrees, Longitude difference=[0.71] degrees.
** ~~~ ** ..Time Zone difference=[0.0] hour(s), Elevation difference=[92.11] percent, [175.00] meters.

Do I need take it into account? If yes, any suggestions?

Second question regarding "Ground temperature".The house have the exterior floor with outside boundary condition Ground, after running simulation I've got warning:

** Warning ** GetSurfaces: Surfaces with interface to Ground found but no "Ground Temperatures" were input.
** ~~~ ** Found first in surface=15183A
** ~~~ ** Defaults, constant throughout the year of (18.0) will be used.

Where should I include Ground temperature, or it should be contain in weather file?

Thanks in advance.

Best regards, Veronika




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___