[Equest-users] Inputing data for terminal boxes....
Jeff Schorsch
jschorsch at hmg-associates.com
Tue Apr 22 09:24:50 PDT 2008
Robby, thank you so much for your time sir. I was almost panicking about how I was going to make these changes. I hope one day I can be of some help to you. Great response!
Jeff
----- Original Message -----
From: Robby Oylear
To: 'Jeff Schorsch'
Sent: Tuesday, April 22, 2008 11:21 AM
Subject: RE: [Equest-users] Inputing data for terminal boxes....
Yes, the wizard is really just a great tool for starting out and giving you a basis for all of your schedules, envelope components, HVAC systems, and your building shell. Once your out of the wizard you can't go back without losing all of your changes. Anything the wizard can do, you can do in the detailed interface, granted it might take a little longer in some cases.
Responding to the main list address is fine.
Robby Oylear
Project Engineer
direct: 206.788.4571
cell: 206.354.2721
www.rushingco.com
------------------------------------------------------------------------------
From: Jeff Schorsch [mailto:jschorsch at hmg-associates.com]
Sent: Tuesday, April 22, 2008 9:18 AM
To: Robby Oylear; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Inputing data for terminal boxes....
Thank you so much for the haste response. I really do appreciate it. So once I have built my building and entered all I can in the building creation wizard, I can just work straight in the detailed interface only without having to return to the wizard?
Also, is this the proper way to respond to the thread?
Thanks
Jeff
----- Original Message -----
From: Robby Oylear
To: 'Jeff Schorsch' ; equest-users at lists.onebuilding.org
Sent: Tuesday, April 22, 2008 10:55 AM
Subject: RE: [Equest-users] Inputing data for terminal boxes....
It is not possible to save the changes you've made in detailed edit mode if you want to return to the wizard, unless you go into the .inp file and copy all of the information that you know you have changed. Most everything you do in the building creation wizard can be done in detailed edit mode so I think your question should really be how do you do what you want done in the wizard in detailed edit mode.
Robby Oylear
Project Engineer
direct: 206.788.4571
cell: 206.354.2721
www.rushingco.com
----------------------------------------------------------------------------
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff Schorsch
Sent: Tuesday, April 22, 2008 8:53 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Inputing data for terminal boxes....
Hi,
I am a new user and I have a few questions. I am still not sure how this message board/posting works and I hope I am doing this right. I have developed my building in the DD Wizard and I have inputed as much information as I can. I have created 6 air handlers that all have single duct VAV boxes with hot water reheat. My question is:
When I go to the Detailed Interface to edit the inputs for the boxes or the air handlers, even just to rename the items, and then return to the Building Creation Wizard it deletes all these changes I made (yes I do get the message warning me). How do I make these inputs remain as I have edited them in the Detailed Interface? I am aware that this may be a very simple, amateur question, but I cant seem to find how to input the more detailed information into the boxes and the air handlers than in the Detailed Interface. And, if I need to go into the Building Creation wizard to make an edit, I dont want to lose all the changes. I have gone through the tutorial, but it does not go into great detail about this (atleast not that I have found yet.). Please Help!!!
Thanks everyone!
JEFF SCHORSCH E.I.T.
HMG & ASSOCIATES
70 N.E. LOOP 410 SUITE 1070
PH.(210)349-0800
FAX.(210)349-2736
jschorsch at hmg-associates.com
www.hmg-associates.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080422/00a5b46e/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1840 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080422/00a5b46e/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1840 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080422/00a5b46e/attachment-0003.jpeg>
More information about the Equest-users
mailing list