[Equest-users] eQuest Warning
Alison Staudinger
astaudinger at jdrm.com
Thu Jul 17 08:37:05 PDT 2008
I had the same warning yesterday and although I cannot explain why the
warning went away, I can tell you what I did and if you're lucky maybe
it will apply for your case as well. I had 'Packaged Single Zone'
specified for my System Type and 'Plenum' for the Return Air Path of the
system parameters and obviously under my plenum zone I had the Zone Type
as 'Plenum'. For this isolated space it wasn't actually a plenum (the
remaining 98% of the building is a VAV RA plenum system) so I changed
the system to a 'Direct' Return Air Path and the Plenum Zone to an
'Unconditioned' Zone Type. After doing that my warning went away. I
don't know why but thought I would share it anyhow. Good luck!
Alison Staudinger P.E., LEED AP
JDRM Engineering
5604 N. Main St.
Sylvania, OH 43560
(419) 824-2400
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Frymire, Nathan
Sent: Wednesday, July 16, 2008 10:45 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest Warning
Hello-
First time posting and glad I found this resource. This is a tricky
software to learn/utilize on projects.
I'm modeling a small office building that we'd like to certify LEED
Silver. Detailed output is giving me the following message for each
zone:
**WARNING***************************************************************
*******
Zone: EL2 South Perim Zn (G.S6) could not
successfully
allocate all equipment energy to the 5-minute bins
because of an equipment overload. The peak load
used in ECONOMICS will not include the fraction due
to the overload, but the PLANT reports will.
Mon/Day/Hour: 12 21 8 Energy: 1.9 Unallocated: 0.250
Does anyone have an idea what this might be or how to correct it? It
must have something to do with a control at the zone level. Any
assistance would be appreciated. Thanks.
Nathan R. Frymire, LEED(r) A.P.
Mechanical Engineer
Burns & McDonnell
9400 Ward Parkway
Kansas City, MO 64114
Phone: 816-822-3900 ext 8513
Fax: 816-822-3423
www.burnsmcd.com <http://www.burnsmcd.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080717/72ea3736/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 3181 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080717/72ea3736/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1418 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080717/72ea3736/attachment-0002.jpeg>
More information about the Equest-users
mailing list