[Equest-users] waterside economizer in eQuest
Fred Porter
FPorter at archenergy.com
Mon Jul 28 14:52:58 PDT 2008
No, that's not required. If the WSE-"Chiller" is listed with the chillers on a loop, DOE-2 will use it when conditions allow. "Conditions" include CHW temperature, so reset up of CHW if possible maximizes the modeled use of the WSE.
>>> Brian Fountain <bfountain at greensim.com> 7/28/2008 2:12 PM >>>
Further to this -- you will likely need to set up your equipment
controls to specify the water economizer chiller type leading in the
winter (below a certain OA) and the regular chillers leading above a
certain OA -- or based on a schedule.
Steve Mignogna wrote:
> You can set up a separate chiller of type "water economizer". This
> will attach to your CHW and CW Loops and will bypass the chiller and
> circulate through your cooling tower when the outside air conditions
> are acceptable for free cooling.
>
>
>
> On Fri, Jul 25, 2008 at 11:13 AM, Marcus Eliason <meliason at essexco.com
> <mailto:meliason at essexco.com>> wrote:
>
>
> Hello,
>
> Can someone please explain the proper way to model a waterside
> economizer in
> eQuest? I have found the option for a cooling tower with HX, but
> this does
> not seem to yield any results.
>
> Thank you,
>
> Marcus Eliason
> Essex Engineering Corporation
> 404.365.9482
> meliason at essexco.com <mailto:meliason at essexco.com>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> --
> Steve Mignogna
> Atelier Ten
> ------------------------------------------------------------------------
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
> ------------------------------------------------------------------------
>
> No virus found in this incoming message.
> Checked by AVG.
> Version: 7.5.524 / Virus Database: 270.5.5/1570 - Release Date: 7/24/2008 6:59 AM
>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080728/d340808a/attachment-0002.htm>
More information about the Equest-users
mailing list