[Equest-users] Spam:Re: Heating problems....
Jay Keazer
JKeazer at tmecorp.com
Tue May 27 06:07:01 PDT 2008
Jeff,
I would check the value of "Reheat Delta T" under Heating > Coil Cap/Control
on your system. This value sets a limit on the change in supply air
temperature as it passes through the terminal unit reheat coils. The default
of 30 F often causes this warning for me. For example if your air handler
discharge temperature is 55 F and your desired zone supply temperature is 100
F, your "Reheat Delta T" would need to be 45 to allow this to happen in the
simulation. The default of 30 would only allow 85 F zone supply air
temperature.
Jay Keazer, EI
Energy Services Division
2039 Green Acres Rd.
Fayetteville, AR 72703
Phone: (479) 521-8634
Fax: (479) 521-1014
www.tmecorp.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff
Schorsch
Sent: Thursday, May 08, 2008 1:12 PM
To: Sheila
Cc: equest-users at lists.onebuilding.org
Subject: Spam:Re: [Equest-users] Heating problems....
Thank you for responding. When I do a simulation it aborts the run, then I
cant see the SS-F / SS-R reports.
----- Original Message -----
From: Sheila <mailto:sheila at energyopportunities.com>
To: Jeff Schorsch <mailto:jschorsch at hmg-associates.com>
Sent: Thursday, May 08, 2008 12:28 PM
Subject: RE: [Equest-users] Heating problems....
Hi Jeff,
How many hours of unmet load do you have for zones served by these
units? See reports SS-F and/or SS-R. I often have these warnings even when
all my zones are conditioning properly. If that is the case, ignore the
warnings and don't waste your time trying to fix them. The nice thing about
SS-F is that it will tell you how cold the zones are getting and the months
unmet load hours occur.
If you have a lot of unmet load hours, I would start checking to see
if my zone thermostat schedules, heating availability schedule, and fan
schedules match. If the hours of unmet load occur during the summer, you
have simultaneous heating and cooling. Try setting the heating thermostat to
55 during the summer months to eliminate the call for heating.
Good luck.
Sheila Sagerer
Energy Engineer, EIT, LEED AP
Energy Opportunities, Inc, a 7group company
Phone: 717-880-9069
www.sevengroup.com
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff
Schorsch
Sent: Thursday, May 08, 2008 12:40 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Heating problems....
This is still my first time creating my simulation and I thought I
was on the right track...
I have a 100% OA unit with a preheat coil and chilled water cooling
coils to maintain a 52 deg off the coil. The zones are
handled by singe duct, straight VAV terminal units with hot water
reheat coils. I have set all
the zone set points to 72 degrees and I am getting a message that
reads as shown below. I have
inputted the heating capacity for the preheat coil and the capacity
for heating in the zonal VAV terminal unit.
Just to see what would happen I grossly oversized the VAV heating
capacity to see if the error would be fixed,
it did not. I checked the LS-B space peak loads and it shows that the
zone heating capacity required is only 25% of what I am inputting. Please
help, I have no clue what I am doing wrong.
**WARNING********************************************************************
**
ZONE TU1-6
might have insufficient heating capability.
Check that the SYSTEM or ZONE HEATING-CAPACITY plus this
ZONEs BASEBOARD-RATING is adequate to maintain the ZONE
specified DESIGN-HEAT-T for the calculated peak ZONE load
(see LS-A or LS-B for the ZONE peak load.)
SYSTEM AHU-1
which supplies the above listed ZONE, has a design heating
coil exit temperature, HEAT-SET-T,(plus any zone reheat)
below its MAX-SUPPLY-T or the ZONE DESIGN-HEAT-T, which
might account for the insufficient heating capability.
Thanks!!!
JEFF SCHORSCH E.I.T.
HMG & ASSOCIATES
70 N.E. LOOP 410 SUITE 1070
PH.(210)349-0800
FAX.(210)349-2736
jschorsch at hmg-associates.com
www.hmg-associates.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080527/baa213db/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 7548 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080527/baa213db/attachment-0002.png>
More information about the Equest-users
mailing list