[Equest-users] CHW Pump differential temperature

Dan Russell danr at engineeringinc.com
Tue Nov 4 08:38:25 PST 2008


John, wouldn't there also be reduced chiller energy due to the pump introducing less heat into loop?

 Dan Russell, EIT

[cid:image001.jpg at 01C93E61.0B5A8000]

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Xavier García Casals
Sent: Friday, October 31, 2008 4:47 AM
To: Aulbach, John
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] CHW Pump differential temperature

Hi,
Probably because the chiller's EIR is reduced due to a more favorable inlet temperature. Have a look at your chiller performance curves in the model.

En/na Aulbach, John ha escrit:
All:

I have run a Base Case and a Parametric run for a Central Plant serving an office complex. Everything in both runs is the same, EXCEPT that the Base run has a 10°F differential temperature and the Parametric run has a 15°F differential temperature. The CHW pump is variable speed.

As expected, electric energy is saved (about 40,000 kWh/year for a 600 ton plant).  However, about 15,000 kWh is saved at the Chilled Water pump, and 22,000 kWh is saved at the chiller.

I changed the Loop Design DT to 15°F and the CHW Coil Design Delta T to 15°F.

Why is my chiller energy reducing?

Thanks.

John R. Aulbach, PE, CEM
Project Manager
Nexant, Inc.
701 West Kimberly Ave., Suite 245
Placentia, CA 92870-6342 USA
Phone: 714-524-4402
Fax: 714-524-4407
email: jaulbach at nexant.com<mailto:jaulbach at nexant.com>







________________________________






_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>



--




Xavier García Casals



Sistemas Solares, Eficiencia Energética e Ingeniería Bioclimática

AIGUASOL INGENIERÍA



Sistemes Avançats d'Energia Solar Tèrmica SCCL

C/ Palermo, 17. Bajos dcha. 28043 Madrid

Tel: (+34) 91 142 27 88



C/ Roger de Llúria,  29 3r 2a 08009 Barcelona

Tel: (+34) 93 342 47 55  Fax: (+34) 93 342 47 56



Mobil: 660 22 94 45

xavier.garcia at aiguasol.coop<mailto:xavier.garcia at aiguasol.coop>

http://www.aiguasol.coop<http://www.aiguasol.coop/>



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081104/596222aa/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 7994 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081104/596222aa/attachment.jpg>


More information about the Equest-users mailing list