[Equest-users] eQuest Space Type Inputs

Jeremy Poling jpoling at epsteinglobal.com
Wed Apr 8 14:33:29 PDT 2009


This is used by the Wizard mode to setup the default load factors, such
as people per zone, lighting power per zone, etc.  The wizards being
primarily setup for quick studies and not really detailed output make
this feature only useful if you never leave the Wizard mode.
Ultimately, I usually override a lot of the wizard default calculations
with actual load calculation values.  Instead of 8.4437 people
calculated by the wizard the zone may have a design occupancy of 7
people.  Lighting power density may be 0.987 w/sf as determined by the
wizard, but I'll input the actual wattage instead.  If it is for LEED,
then I run some of these calcs separately and tell eQuest the value.

 

My e-mail address has changed.
Please update your records using the information provided below.

Jeremy R. Poling, LEED AP
Senior Sustainability Analyst
Strategic Services

Site Solutions | Operations | Sustainability

EPSTEIN
Architecture
Interiors
Engineering
Construction

600 West Fulton Street
Chicago, Illinois 60661-1259

D (312) 429-8152
F (312) 559-1217
C (312) 504-5905
jpoling at epsteinglobal.com <mailto:jpoling at epsteinglobal.com> 

www.epsteinglobal.com <http://www.epsteinglobal.com/> 

We are proud to announce that our collective companies, A. Epstein and
Sons International, Inc., Interior Space International, annex|5 and neXt
wayfinding + design are now simply known as Epstein.

Epstein is a firm believer in sustainability. We ask that you please
consider the environment before printing this e-mail.

________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Matutinovic, Luka
Sent: Wednesday, April 08, 2009 3:22 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest Space Type Inputs

 

Hello,

 

I have a question regarding eQuest space type inputs.  I typically
create zones in the Wizard by tracing imported CAD drawings and zoning
according to perimeter/core, same HVAC system, similar loads or space
types.  However, when I get to the Activity Area Allocation screen
(screen 13 in the envelope wizard), I have to assign a percentage of
each space type to ALL the zones.  Once in the detailed mode, if I check
a particular zone, it says for example Office (67%).  Can I change this?

 

Is there a way to assign each zone only one space type and over-ride
this average area blending business.  It seems like a bad way to
correctly account for different space uses.  I guess the more important
question is: does it really matter?  I know eQuest allows you to assign
space types either to perimeter or core or both, so there was a
conscious decision to allocate space types based on perimeter and core
and I understand the rationale since internal and external loads are
quite different.  But why stop there? Why not allow full flexibility to
assign each zone a unique space type? 

 

Thanks,

 

Luka Matutinovic, B.A.Sc., LEED(r) AP

Green Building Consultant
 
T. 416.487.5257 ext. 317  
F. 416.487.9766  
Toll Free 1.888.425.7255
www.halsall.com 

HALSALL ASSOCIATES LTD. 
Toronto  Richmond Hill  Ottawa  Sudbury 
Burlington  Calgary  Vancouver  Dubai 

'50 Best Workplaces in Canada' 
2008 Globe and Mail

P Please consider the environment before printing this e-mail

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090408/8626bb1a/attachment-0002.htm>


More information about the Equest-users mailing list