[Equest-users] error OA from System

Brahme, Rohini UTRC BrahmeR at utrc.utc.com
Fri Aug 7 08:38:55 PDT 2009


You can do this in the .inp file - just cut the oa system description and paste it before the system that uses it.

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Verena Kindl
Sent: Friday, August 07, 2009 11:31 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] error OA from System

 


Hi ,

i modeled a FCU which is getting the outside air from the corridor (SZRH) in the detailed mode i changed the minimum outside air ratio to 0 and i put in outside air from system SZRH. When i want to run the simulation i get the error

ERROR***********************************************************************

EL1 Sys1 (FC) (G.E4) defined before its OA-FROM-SYSTEM. This

will cause incorrect OA temperature calculation. Move this SYSTEM to be

defined before its OA-FROM-SYSTEM in the project BDL input file.

Can anybody help me with it i do not know how i can move the system ??

< P>Thanks

 

 

Neu: WEB.DE Doppel-FLAT mit Internet-Flatrate + Telefon-Flatrate   
für nur 19,99 Euro/mtl.!* http://produkte.web.de/go/02/ <http://produkte.web.de/go/02/>   

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090807/cb057881/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 332 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090807/cb057881/attachment-0002.jpeg>


More information about the Equest-users mailing list