[Equest-users] error OA from System

B. Fountain bfountain at greensim.com
Fri Aug 7 08:40:34 PDT 2009


You will need to close eQUEST and edit the .inp file in a text editor. 
Move the "from" system (with its child zones) to be the first system on
the list. Then you can reopen eQUEST and it will be at the top of the
list.



>
>
>
> Hi ,
>
> i modeled a FCU which is getting the outside air from the corridor (SZRH)
> in the detailed mode i changed the minimum outside air ratio to 0 and i
> put in outside air from system SZRH. When i want to run the simulation i
> get the error
>
> ERROR***********************************************************************
>
> EL1 Sys1 (FC) (G.E4) defined before its OA-FROM-SYSTEM. This
>
> will cause incorrect OA temperature calculation. Move this SYSTEM to be
>
> defined before its OA-FROM-SYSTEM in the project BDL input file.
>
> Can anybody help me with it i do not know how i can move the system ??
>
> Thanks
>
>
>
> Neu: WEB.DE Doppel-FLAT mit Internet-Flatrate + Telefon-Flatrate
> für nur 19,99 Euro/mtl.!* *http://produkte.web.de/go/02/*
> [http://produkte.web.de/go/02/]
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>





More information about the Equest-users mailing list