[Equest-users] Enthalpy wheels
Cam Fitzgerald
cam at energyopportunities.com
Wed Aug 12 05:21:57 PDT 2009
Tom:
If you have economizer controls for your unit, you need to disable the wheel
during the temperate months to reap the benefits of the economizer or your
cooling load WILL go up.
Cam S. Fitzgerald, PE, LEED AP
Energy Opportunities, LLC
a 7group company
phone: (717) 292-2636 x11
fax: (717) 292-0585
e-mail: fitzgerald at sevengroup.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Tom
Lawrence
Sent: Tuesday, August 11, 2009 2:57 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Enthalpy wheels
We are trying to model a building with enthalpy wheel OA energy recovery.
After completing the entire model and getting all set up in detailed edit
mode, when we add in an enthalpy wheel for even just one zone, the cooling
energy increases. Heating energy does decrease.
We tried to:
1. Control sequence of operation for OA exhaust delta enthalpy (also same
result if control when fans on and control by differential T)
2. As a test, it made no difference if it was enthalpy wheel, sensible
wheel, enthalpy HX, sensible HX or heat pipe... same story with cooling
increased.
3. Even with fan pressure rise set to '0' (no fan energy), cooling
increased.
We have tried a multitude of combinations and keep getting similar results.
Tom Lawrence, Ph.D., P.E., LEED-AP
Public Service Associate, Faculty of Engineering
Driftmier Engineering Center
University of Georgia
Athens, GA 30602
(706) 542-4322
lawrence at engr.uga.edu
"The only thing you take with you when you're gone is what you leave
behind." - John Allston
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090812/cc5a312e/attachment-0002.htm>
More information about the Equest-users
mailing list