[Equest-users] Chemistry Laboratory Model

Vikram Sami VSami at lasarchitect.com
Mon Dec 7 10:22:55 PST 2009


That's a good point Paul

 

Vikram Sami, LEED AP 
Direct Phone 404-253-1466 | Direct Fax 404-253-1366 

LORD, AECK & SARGENT ARCHITECTURE



 

From: Paul Erickson [mailto:perickson at aeieng.com] 
Sent: Monday, December 07, 2009 1:21 PM
To: Vikram Sami; Kugler, Nicholas; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Chemistry Laboratory Model

 

I'd like to add to Vikram's comment about CAV hoods.  I'd encourage you
to advocate for VAV hoods if the zone's hood CFM is 2ACH or greater.
There has been a lot of progress in recent years in working towards
lower occupied and unoccupied ACH minimums, and 2 ACH may be within
reason for many clients in the coming years.  If VAV hoods are in place,
and the capabilities of the air valves allow, the system would be able
to turn down to a lower ACH minimum and garner your client savings.

 

Paul 

 

Paul Erickson  LEED(r) AP 
Sustainable Practice Leader

 

AEI | AFFILIATED ENGINEERS, INC.  
5802 Research Park Blvd. | Madison, WI  53719

P: 608.236.1112 | F: 608.238.2614  
perickson at aeieng.com <mailto:perickson at aeieng.com>   |  www.aeieng.com
<http://www.aeieng.com>   

 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vikram
Sami
Sent: Monday, December 07, 2009 11:51 AM
To: Kugler, Nicholas; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Chemistry Laboratory Model

 

Nick,

The way I would approach this:

 

1.       Establish what the minimum flow rate for each hood is (as a
percentage of maximum). Most chemical hoods have a minimum required cfm
rate even when closed that flows through the reagent shelf below to keep
it ventilated. 

2.       Establish a diversity schedule for the hoods

3.       In eQUEST v3.63 and above you can specify airflow tracking for
exhaust air streams on a thermal zone basis - there's a good help
section on what the different tracking options do. It's my understanding
that this was put in specifically for fumehoods. Set your max flow rate
here and set up a fraction schedule to determine flow rate. 

 

One thing you might want to check up on is the fumehood density. If the
lab is very fumehood intensive, then it might make sense to go with the
VAV hoods. However, if it's a ventilation driven lab (as opposed to an
exhaust driven lab), you might as well have constant volume hoods. 

 

For instance, if your EHS requires 6 air changes per hour in a 10 foot
high 10,000ft2 lab, your supply cfm = 10,000 cfm. Lets say you have 10 x
6' wide fumehoods with 800cfm at max sash height (18"). That would give
you 8,000 cfm. So having VAV controls on the hoods is not going to
reduce your airflow unless you ramp down to below 5ACH during unoccupied
hours. 

 

Hope this helps

Vikram Sami, LEED AP 
Direct Phone 404-253-1466 | Direct Fax 404-253-1366 

LORD, AECK & SARGENT ARCHITECTURE

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kugler,
Nicholas
Sent: Monday, December 07, 2009 7:42 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Chemistry Laboratory Model

 

I am about to begin an energy model for a large university lab project
that includes about 150 VAV chemical fume hoods. The building systems
will include a true VAV exhaust system, not a bypass system. Please
advise how this can be modeled using eQuest. Thank you in advance.

 

Nick Kugler, LEED AP

Mechanical Engineering

 

TLC Engineering for Architecture
Your Architecture 2030 Partner

 

874 Dixon Boulevard

Cocoa, FL 32922

 

phone: 

321-636-0274

fax: 

321-639-8986

website: 

www.tlc-engineers.com <http://www.tlc-engineers.com> 

 

  <http://www.tlc-engineers.com/> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091207/5a975eaa/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 5272 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091207/5a975eaa/attachment-0002.gif>


More information about the Equest-users mailing list