[Equest-users] Chemistry Laboratory Model
Kugler, Nicholas
nicholas.kugler at tlc-eng.com
Wed Dec 9 04:35:28 PST 2009
Thank you all for your input. The building exhaust systems will be separated into 4 components: general exhaust, fume hood exhaust, snorkel exhaust and biological safety exhaust. The reason for this is for cross contamination considerations in the non-general exhaust systems and the goal to achieve total energy recovery with a energy recovery wheel. In addition, the systems will have different static pressure requirements. Yes, I am implementing airside heat recovery for the general exhaust system, and considering application for the fume hood system depending on feasibility of a system with no cross contamination as required by the owner.
Bill - I am planning on having variable flow at the system level for both the general exhaust and fume hood exhaust systems. This is precisely why I was concerned with the software's ability to model this situation. Thank you for your advice.
Nick Kugler, LEED AP
Mechanical Engineering
From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com]
Sent: Monday, December 07, 2009 2:49 PM
To: Kugler, Nicholas; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Chemistry Laboratory Model
Nick,
Are you considering/planning to use heat recovery through system-level variable flow exhaust system(s)? If so, I don't think it will work if you model zonal exhaust air flow tracking. (Someone please correct me if you have determined otherwise.) One way you can model variable hood exhaust and allow for energy recovery is to use a MIN-AIR-SCH at the system level to vary the percentage of outside air, in combination with MIN-FLOW-SCH at the zone level, provided your system is VAV. I would add total system supply flow and O/A percentage to your hourly reports, so you can see what the system is doing throughout the year.
Regards,
Bill
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vikram Sami
Sent: Monday, December 07, 2009 1:25 PM
To: Paul Erickson; Kugler, Nicholas; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Chemistry Laboratory Model
Oops - hit send before I finished typing.
What I meant to say was - that's a really good point Paul. You can set up your CAV hoods to be 2 steps - for unoccupied and occupied hours too if that is the situation. We end up doing that on a lot of projects.
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
From: Paul Erickson [mailto:perickson at aeieng.com]
Sent: Monday, December 07, 2009 1:21 PM
To: Vikram Sami; Kugler, Nicholas; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Chemistry Laboratory Model
I'd like to add to Vikram's comment about CAV hoods. I'd encourage you to advocate for VAV hoods if the zone's hood CFM is 2ACH or greater. There has been a lot of progress in recent years in working towards lower occupied and unoccupied ACH minimums, and 2 ACH may be within reason for many clients in the coming years. If VAV hoods are in place, and the capabilities of the air valves allow, the system would be able to turn down to a lower ACH minimum and garner your client savings.
Paul
Paul Erickson LEED(r) AP
Sustainable Practice Leader
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI 53719
P: 608.236.1112 | F: 608.238.2614
perickson at aeieng.com<mailto:perickson at aeieng.com> | www.aeieng.com<http://www.aeieng.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vikram Sami
Sent: Monday, December 07, 2009 11:51 AM
To: Kugler, Nicholas; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Chemistry Laboratory Model
Nick,
The way I would approach this:
1. Establish what the minimum flow rate for each hood is (as a percentage of maximum). Most chemical hoods have a minimum required cfm rate even when closed that flows through the reagent shelf below to keep it ventilated.
2. Establish a diversity schedule for the hoods
3. In eQUEST v3.63 and above you can specify airflow tracking for exhaust air streams on a thermal zone basis - there's a good help section on what the different tracking options do. It's my understanding that this was put in specifically for fumehoods. Set your max flow rate here and set up a fraction schedule to determine flow rate.
One thing you might want to check up on is the fumehood density. If the lab is very fumehood intensive, then it might make sense to go with the VAV hoods. However, if it's a ventilation driven lab (as opposed to an exhaust driven lab), you might as well have constant volume hoods.
For instance, if your EHS requires 6 air changes per hour in a 10 foot high 10,000ft2 lab, your supply cfm = 10,000 cfm. Lets say you have 10 x 6' wide fumehoods with 800cfm at max sash height (18"). That would give you 8,000 cfm. So having VAV controls on the hoods is not going to reduce your airflow unless you ramp down to below 5ACH during unoccupied hours.
Hope this helps
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kugler, Nicholas
Sent: Monday, December 07, 2009 7:42 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Chemistry Laboratory Model
I am about to begin an energy model for a large university lab project that includes about 150 VAV chemical fume hoods. The building systems will include a true VAV exhaust system, not a bypass system. Please advise how this can be modeled using eQuest. Thank you in advance.
Nick Kugler, LEED AP
Mechanical Engineering
TLC Engineering for Architecture
Your Architecture 2030 Partner
874 Dixon Boulevard
Cocoa, FL 32922
phone:
321-636-0274
fax:
321-639-8986
website:
www.tlc-engineers.com<http://www.tlc-engineers.com>
[cid:image001.gif at 01CA789F.B932FC60]<http://www.tlc-engineers.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091209/c85c564a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 5272 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091209/c85c564a/attachment-0002.gif>
More information about the Equest-users
mailing list