James,
You'll need to edit the .inp file instead of the .bdl file. The .bdl file
is generated from the .inp & .pd2 files, and changes made to it will be
discarded every time you save the project.
You'll need to create a new zone and reference the space in question either
from the .inp file or the equest interface.
Steven
Steven Savich
Systems West Engineers
411 High Street
Eugene, OR 97401-2427
(541) 342-7210
(541) 342-7220 (fax)
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James D.
Waechter
Sent: Monday, February 02, 2009 7:39 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] space has no ZONE - one is required
All,
On the baseline model for a project, I continue to get the following error
despite several attempts to remedy: SPACE E13 NNW Perim Spc (M.NNW51) has no
ZONE - one is required.
My attempts to fix it have included:
* trying to locate a ZONE definition within the program - unsuccessful
* directly editing the BDL file by pasting a missing section from the
Proposed BDL file - didn't work; errored out anyway (see below)
* deleting the error at the end of the BDL file - didn't work; errored
out anyway
I've included the text below from the Designed (proposed) BDL file. I
believe the bolded text is what is missing from the Baseline BDL file.
The text below is from the Baseline BDL file indicating where I think the
missing text would go.
*90096* SPACE = "E13 North Perim Spc (M.N50)"
*91135* "E13 Sys2 (PMZS) (M.N50)" = SYSTEM
*90097* ..
*91136* TYPE = PTAC
*90098* "E13 Sys2 (FC) (M.NNW51)" = SYSTEM
*91137* HEAT-SOURCE = HOT-WATER
*90099* TYPE = FC
*91138* BASEBOARD-SOURCE = NONE
*90100* HEAT-SOURCE = HOT-WATER
*91139* SIZING-RATIO = 1
*90101* BASEBOARD-SOURCE = NONE
*91140* HEAT-SIZING-RATI = 1.25
*90102* SIZING-RATIO = 1.15
*91141* COOL-SIZING-RATI = 1.15
*90103* MAX-SUPPLY-T = 95
*91142* MAX-SUPPLY-T = 90
*90104* MIN-SUPPLY-T = 55
*91143* MIN-SUPPLY-T = 55
*90105* ECONO-LIMIT-T = 65
*91144* FAN-SCHEDULE = "S2 Sys2 (PMZS) Fan Sch"
*90106* OA-CONTROL = FIXED
*91145* FAN-CONTROL = FAN-EIR-FPLR
*90107* FAN-SCHEDULE = "S2 Sys2 (FC) Fan Sch"
*91146* SUPPLY-STATIC = 0.15
*90108* SUPPLY-STATIC = 0.5
*91147* SUPPLY-EFF = 0.507515
*90109* SUPPLY-EFF = 0.328
*91148* HW-VALVE-TYPE = TWO-WAY
*90110* HW-VALVE-TYPE = TWO-WAY
*91149* HW-COIL-DT = 50
*90111* HW-LOOP = "Hot Water Loop"
*91150* HW-LOOP = "Hot Water Loop"
*90112* CHW-VALVE-TYPE = TWO-WAY
*91151* COOLING-EIR = 0.3667
*90113* CHW-LOOP = "Chilled Water Loop"
*91152* FURNACE-HIR = 1.24067
*90114* FURNACE-HIR = 1.24067
*91153* ..
*90115* ..
>>>INSERT MISSING TEXT HERE<<<
*90116* "E13 NNW Perim Zn (M.NNW51)" = ZONE
*91154* "E13 North Perim Zn (M.N50)" = ZONE
*90117* TYPE = CONDITIONED
*91155* TYPE = CONDITIONED
*90118* MIN-FLOW-RATIO = 1
*91156* MIN-FLOW-RATIO = 1
*90119* FLOW/AREA = 0.5
*91157* FLOW/AREA = 0.5
*90120* OA-FLOW/PER = 1.0846
*91158* OA-FLOW/PER = 1.0846
*90121* DESIGN-HEAT-T = 72
*91159* DESIGN-HEAT-T = 72
*90122* HEAT-TEMP-SCH = "S2 Sys2 (FC) Heat Sch"
*91160* HEAT-TEMP-SCH = "S2 Sys2 (PMZS) Heat Sch"
*90123* DESIGN-COOL-T = 75
*91161* DESIGN-COOL-T = 75
*90124* COOL-TEMP-SCH = "S2 Sys2 (FC) Cool Sch"
*91162* COOL-TEMP-SCH = "S2 Sys2 (PMZS) Cool Sch"
*90125* SIZING-OPTION = ADJUST-LOADS
*91163* SIZING-OPTION = ADJUST-LOADS
*90126* SPACE = "E13 NNW Perim Spc (M.NNW51)"
*91164* SPACE = "E13 North Perim Spc (M.N50)"
*90127* ..
*90128* "E13 Sys2 (FC) (M.C52)" = SYSTEM
Please let me know of any thoughts or suggestions you may have. Any help is
appreciated.
Regards,
James D. Waechter, P.E., LEED A.P.
Beaudin Ganze Consulting Engineers
P 303.278.3820 x 5246
F 303.278.3843
<http://www.bgce.com/> 76% of Staff LEED Accredited Professionals!
P Please consider the environment before printing
--
This message has been scanned for viruses and
dangerous content by <http://www.mailscanner.info/> MailScanner, and is
believed to be clean.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090202/faf4baed/attachment-0002.htm>
More information about the Equest-users
mailing list