[Equest-users] adjoining spaces in different shells
Patrick Darby
pdarby at twfp.com
Mon Jan 12 12:53:26 PST 2009
This is a situation I have come across in the past. To resolve this
issue, I deleted the exterior walls created where the shells met and
created an interior wall, in one of the spaces, in there place. If there
is actually an interior wall here you should leave the "wall type" as
Standard and ensure you specify the "Next To" command to the adjoining
space.
If there is no wall here whatsoever, specify the "wall type" as Air and
again make sure you specify the "Next To" command to the adjoining
space.
Hope this helps,
Patrick Darby, BScE
Mechanical Engineering Services
The Walter Fedy Partnership
Phone: 519-576-2150 x271
Fax: 519-576-5499
Web: www.twfp.com
The information contained in this e-mail is intended only for the individual or entity to whom it is addressed. Its contents (including any attachments) may contain confidential and/or privileged information. If you are not an intended recipient you must not use, disclose, disseminate, copy or print its contents. If you receive this e-mail in error, please notify the sender by reply e-mail and permanently delete the message. Information, opinions or conclusions contained in this message that do not relate to the official business of "The Walter Fedy Partnership" will be understood as neither given nor endorsed by it.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/fb62c232/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: twfp.jpg
Type: image/jpeg
Size: 8530 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/fb62c232/attachment-0002.jpg>
More information about the Equest-users
mailing list