[Equest-users] EQUEST Partially Below Grade Wall

Robert.N.Degrasse at jci.com Robert.N.Degrasse at jci.com
Mon Jan 12 15:33:26 PST 2009


Brian: In the DD wizzard, can you create a shell 4'below grade and then 
create a second shell directly above the first shell that is above grade 
of whatever height is required? 



Brian Fountain <bfountain at greensim.com> 
Sent by: equest-users-bounces at lists.onebuilding.org
01/12/2009 01:58 PM

To
Ryan Lacey <ryan at petersenengineering.com>, 
"equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
cc

Subject
Re: [Equest-users] EQUEST Partially Below Grade Wall






As you have guessed, you cannot do this in the wizard.  So, in the wizard, 
create the u/g wall.  Then in detailed mode, set the u/g wall height to 
5'.  Then create new exterior walls (copying upper walls) and set their 
height to 4' with their Z value at 5' -- one for each side of the basement 
as appropriate, linked to the appropriate vertex.

It sounds complicated but is fairly straight forward when you get going. 

Bonne chance,
Brian

Ryan Lacey wrote: 
Hello,
I need to model a wall that is partially below grade.  My basement is only 
about 4? below grade & using the wizard so far I cant figure out a way to 
represent this.  What is the easiest way to go about this?  I am trying to 
stay in the wizard as long as possible. 
 

 

 
Thanks,
 
Ryan Lacey
LEED AP
Petersen Engineering, Inc.
PO Box 4774
6 Market Square
Portsmouth, NH 03801
Phone 603.436.4233 x113
Fax 603.436.4294
www.petersenengineering.com
ryan at petersenengineering.com
 


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to 
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
 


No virus found in this incoming message.
Checked by AVG. 
Version: 7.5.552 / Virus Database: 270.10.5/1885 - Release Date: 1/9/2009 
7:59 PM
 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to 
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/1e15297c/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 6924 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/1e15297c/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 16340 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/1e15297c/attachment-0005.jpeg>


More information about the Equest-users mailing list