[Equest-users] Cooking and Elevators/Escalators
Cam Fitzgerald
cam at energyopportunities.com
Tue Jan 20 05:42:20 PST 2009
Actually, the elevator equipment should be entered in the appropriate
space(s) similar to the kitchen equipment load since it contributes to the
cooling load for the building.
Cam S. Fitzgerald, PE
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Steven
Savich
Sent: Monday, January 19, 2009 11:35 AM
To: 'Soham Babu'; equest-users at lists.onebuilding.org
Cc: 'Sunil Rao'
Subject: Re: [Equest-users] Cooking and Elevators/Escalators
Elevator and exterior lighting loads should be attached directly to the
electric meter. In the detailed interface it's Utility & Economics
tab>Electric Meter>Direct Loads. You'll need to create an elevator schedule
and an exterior lighting schedule. The newest version of eQuest (3.63) has
photocell control for exterior lighting to simply your ext lighting
schedule. I believe the photocell control setup is spelled out in the help
files.
The kitchen equipment load(s) should be entered in the appropriate spaces.
Make sure that you specify the sensible/latent ratio, otherwise it defaults
to 100% sensible.
Steven Savich
Systems West Engineers
411 High Street
Eugene, OR 97401-2427
(541) 342-7210
(541) 342-7220 (fax)
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Soham Babu
Sent: Monday, January 19, 2009 5:32 AM
To: equest-users at lists.onebuilding.org
Cc: Sunil Rao
Subject: [Equest-users] Cooking and Elevators/Escalators
Hi All,
Can you please share where do we get information of cooking and
Elevators/Escalators in Equest.
We have following information
1. Total Connected Load for kitchen/cooking equipment. - plug load.
321.7Kw
2. Total Connected Load for exterior lighting. - plug load. 8.5Kw
3. Elevator horsepower. 25 HP for design.
Let me know where do we have to input these numbers in the detailed mode of
Equest file.
Will appreciate your help
Soham
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090120/8964bbd1/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 42067 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090120/8964bbd1/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 47541 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090120/8964bbd1/attachment-0005.jpeg>
More information about the Equest-users
mailing list