I'm modeling a hotel with ERUs that provide OA directly to each guest room
(at neutral conditions) in which a PTAC conditions and recirculates the air
at the design temperatures (72/75). I have the ERUs providing OA to a dummy
zone without internal loads at different temperatures (76/89). My question
is when the ERU is exhausting, how can I tell it to exhaust the conditioned
air from the guest rooms instead of the OA that it is directly supplying to
the dummy zone? My ERU should technically be exhausting air around 76deg F,
but I have a feeling that it would just be exhausting the same temperature
air that it is supplying to the dummy zone.
I'm also seeing a larger than expected summer heating load on these units,
which may or may not be caused by my question above.
Any help would be much appreciated.
Tracie Monfort
MAIN:
(704) 348-2993
LEEDR AP/Mechanical Designer
FAX:
(704) 348-2995
<mailto:tracie.monfort at hesm.com> tracie.monfort at hesm.com
Cell:
(770) 778-4229
HESM&A Consulting Engineers, Inc.
<http://www.hesm.com/> www.hesm.com
"Engineering the Built Environment"
P Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090326/125de0f0/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2305 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090326/125de0f0/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: aLoft Hotel.BDL
Type: application/octet-stream
Size: 1559270 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090326/125de0f0/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: aLoft Hotel.inp
Type: application/octet-stream
Size: 1007999 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090326/125de0f0/attachment-0001.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: aLoft Hotel.pd2
Type: application/octet-stream
Size: 131073 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090326/125de0f0/attachment-0002.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ERU-1 schematic.pdf
Type: application/pdf
Size: 85760 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090326/125de0f0/attachment.pdf>
More information about the Equest-users
mailing list