[Equest-users] Detailed Data Edit Disappearing
Chris Wark
cwark at rumseyengineers.com
Wed Mar 25 09:06:33 PDT 2009
There are a few things that can only be done (or at least reasonably
done) in wizard mode, so the workaround for this is to save the model
under a new filename, make changes in wizard mode, save the new model to
create the new Input file, then copy all the sections that you didn't
want changed from the old model Input file to the new one. You have to
use the Input files, not the BDL files. I have done this a couple of
times when changing HVAC system types or calculating new wall assembly
U-values but wanting to keep all the windows that I entered in detailed
mode.
Christopher Wark
Project Engineer
___________________________
RUMSEY
E N G I N E E R S
Energy Efficient Design
99 Linden Street
Oakland CA 94607
510 663 2070 x 239
fax 510 663 2080
cwark at rumseyengineers.com <mailto:eswalley at rumseyengineers.com>
www.rumseyengineers.com <http://www.rumseyengineers.com/>
___________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen
Walkerman
Sent: Wednesday, March 25, 2009 6:21 AM
To: Duane Harman
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Detailed Data Edit Disappearing
if you are using any wizards after making detailed data edit changes,
including the EEP wizards, your detailed data edits will be
over-written. Once you go to detailed mode, you pretty much need to
stay there.
--
Karen
On Wed, Mar 25, 2009 at 9:11 AM, Duane Harman <dharman at cyntergyaec.com>
wrote:
I seem to have problems with my input information disappearing in the
detailed data edit and the default values being restored. Examples
would be adding an ERV or modifying the electric utility rates. Am I
navigating through it wrong and deleting the input changes? Not sure
why it disappears.
Duane Harman, PE, CGD
Senior Mechanical Engineer
Cyntergy AEC
320 S. Boston, 12th Floor
Tulsa, OK 74103
TEL: (918) 877-6000
FAX:(918) 877-4000
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090325/0d0b64c6/attachment-0002.htm>
More information about the Equest-users
mailing list