[Equest-users] Exterior Lighting
Paul Riemer
Paul.Riemer at dunhameng.com
Fri May 1 08:12:42 PDT 2009
The exterior lighting load w/sf input in the Wizard will be multiplied by the building area (all floors) to become a direct kW load on the electric meter.
After you finish the wizard, it will be visible on the electric meter under the Utility & Economics tab in the component tree view. In wizard mode, you can view it there. In detailed mode, you can edit it there.
Paul Riemer
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Matutinovic, Luka
Sent: Friday, May 01, 2009 9:57 AM
To: David Dowling; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Exterior Lighting
I believe that facade area should be used. I would assume eQuest would calculate the total lighting power based on total wall area. You can easily check this by specifying 1 W/ft2, attaching a separate meter for exterior lighting and confirming that the numbers make sense based on total wall area obtained from the LV-D report . There are also additional ASHRAE requirements for site lighting.
Luka Matutinovic, B.A.Sc., LEED(r) AP
Green Building Consultant
T. 416.487.5257 ext. 317
F. 416.487.9766
Toll Free 1.888.425.7255
www.halsall.com
HALSALL ASSOCIATES LTD.
Toronto Richmond Hill Ottawa Sudbury
Burlington Calgary Vancouver Dubai
'Best Workplaces in Canada'
2009 Globe and Mail
P Please consider the environment before printing this e-mail
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Dowling
Sent: Friday, May 01, 2009 10:53 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Exterior Lighting
For exterior lighting, does any one know what area is used when applying the W/ft2? I do not see a way to define an external lighting area. Any information on this would be greatly appreciated.
Thank you,
[cid:image001.jpg at 01C9CA44.8539BBB0]
David Dowling
Mechanical Designer
WEST PLAINS ENGINEERING, INC.
1750 Rand Road
Rapid City, SD 57702
Phone: (605) 348-7455 Fax: (605) 348-9445
david.dowling at westplainsengineering.com<mailto:david.dowling at westplainsengineering.com>
www.westplainsengineering.com<http://www.westplainsengineering.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090501/b84e3e4f/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4427 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090501/b84e3e4f/attachment-0001.jpg>
More information about the Equest-users
mailing list