[Equest-users] Heat recovery issues
B. Fountain
bfountain at greensim.com
Thu May 14 06:28:20 PDT 2009
Note that the eQUEST default control for heat recovery is "Float" which
maximizes heat recovery at all times. Consider changing this to "Mixed
Air Reset" where heat recovery will be modulated, allowing economizer free
cooling when applicable.
> I seem to be running into a slight problem getting the heat recovery
> system to work. Right now I have it set as a sensible wheel with an
> airflow of 35315 cfm and an efficiency of 60% (all according to the
> specifications given to me). Unfortunately, using the heat exchanger
> actually causes my energy consumption to increase. Do you have any idea
> why this might be happening and what I can do to fix it?
>
>
> Rebecca Grove, LEED AP
> Senior Engineer
> Thornton Tomasetti
> One Audubon Street, Fourth Floor
> New Haven, CT 06511
> T 203.672.1390 F 203.672.1391
> D 203.672.1436
> RGrove at ThorntonTomasetti.com
> www.ThorntonTomasetti.com
>
> <><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>
> The information in this email and any attachments may contain
> confidential information that is intended solely for the
> attention and use of the named addressee(s). This message or
> any part thereof must not be disclosed, copied, distributed
> or retained by any person without authorization from the
> addressee. If you are not the intended addressee, please
> notify the sender immediately, and delete this message.
> <><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
More information about the Equest-users
mailing list