[Equest-users] Number of heating hours not met
David Dowling
David.Dowling at WestPlainsEngineering.com
Fri May 15 08:37:29 PDT 2009
I thought I would let every one know what solution was for this
particular problem incase you have encountered this error. For
starters, ASHRAE 90.1-2004 in regards to the baseline building is rather
vague on how to assign the specified system to the building, ie. system
per zone, system per site, system per shell etc. I used system per site
since it gave me a slightly better percent improvement over the baseline
model. This assumption was incorrect since a DX cooling with a gas
fired furnace system is not typically selected as a system per site, or
at least I can't think of a situation where this would be the case.
I also noticed that the first zone created within the wizard interface
was the zone where the thermostat set point was tied to, thus resulting
in the error; this is true, since none of the spaces were being
conditioned since the first zone created was satisfied.
David Dowling
Mechanical Designer
WEST PLAINS ENGINEERING, INC.
1750 Rand Road
Rapid City, SD 57702
Phone: (605) 348-7455 Fax: (605) 348-9445
david.dowling at westplainsengineering.com
<mailto:david.dowling at westplainsengineering.com>
www.westplainsengineering.com <http://www.westplainsengineering.com/>
________________________________
From: Charles Land [mailto:cland at geo-marine.com]
Sent: Wednesday, May 13, 2009 9:43 AM
To: David Dowling
Subject: RE: [Equest-users] Number of heating hours not met
Your welcome. Sorry I haven't checked my email in a while.
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David
Dowling
Sent: Wednesday, May 13, 2009 10:12 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Number of heating hours not met
I think I might have figured it out and thank you Charles for directing
me to the system type.
I originally had the system set up as system per site. I just now
changed it to system per zone and it seemed to remove the error. It
also dropped the percentage any system zone is out side the throttling
range from 100 to 3.5.
David Dowling
Mechanical Designer
WEST PLAINS ENGINEERING, INC.
1750 Rand Road
Rapid City, SD 57702
Phone: (605) 348-7455 Fax: (605) 348-9445
david.dowling at westplainsengineering.com
www.westplainsengineering.com <http://www.westplainsengineering.com/>
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David
Dowling
Sent: Wednesday, May 13, 2009 7:46 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Number of heating hours not met
I am using the ASHRAE 90.1-2004 compliant system number 3 which happens
to be DX Coils with Furnace.
David Dowling
Mechanical Designer
WEST PLAINS ENGINEERING, INC.
1750 Rand Road
Rapid City, SD 57702
Phone: (605) 348-7455 Fax: (605) 348-9445
david.dowling at westplainsengineering.com
www.westplainsengineering.com <http://www.westplainsengineering.com/>
________________________________
From: Charles Land [mailto:cland at geo-marine.com]
Sent: Wednesday, May 13, 2009 6:12 AM
To: David Dowling; equest-users at lists.onebuilding.org
Subject: RE: Number of heating hours not met
What type of systems are you using?
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David
Dowling
Sent: Tuesday, May 12, 2009 6:32 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Number of heating hours not met
I have a question concerning a warning related to the number of heating
hours not met and apologize in advance if this topic has been covered
before. The warning I am getting is:
"Zone might have insufficient heating capability. Check that the system
or zone HEATING-CAPACITY plus this zones BASEBOARD-RATING is adequate to
maintain the zone specified DESIGN-HEAT-T for the calculated peek zone
load (see LS-A or LS-B for the zone peak load)."
I am using the auto sizing function within eQuest so I am not
understanding why the spaces are not satisfied. Dose anyone know how to
make the auto size function work to satisfy each zone?
David Dowling
Mechanical Designer
WEST PLAINS ENGINEERING, INC.
1750 Rand Road
Rapid City, SD 57702
Phone: (605) 348-7455 Fax: (605) 348-9445
david.dowling at westplainsengineering.com
www.westplainsengineering.com <http://www.westplainsengineering.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090515/e17d7375/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4427 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090515/e17d7375/attachment-0002.jpeg>
More information about the Equest-users
mailing list