[Equest-users] Loop Operation
Sethi, Amarpreet
amarpreet.sethi at stantec.com
Sat Nov 21 15:51:20 PST 2009
Karen,
I've faced the same problem and as a quick fix, I found best to undersize the condenser water loop till the differential was aggreeable, like you said 10F or so, this as you mentioned reduced the pump energy by a quarter. I'm sure there is a more correct way to do this, please share once you figure it out.
Regards,
Amarpreet
Stantec
stantec.com <http://www.stantec.com/>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
________________________________
From: Karen Walkerman [mailto:kwalkerman at gmail.com]
Sent: Friday, November 20, 2009 12:12 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Loop Operation
Hi All,
I'm having some issues with loop and pump operation in eQuest.
I have tested this issue with water loop heat pump loops. Basically, I set my loop design DT, but for many hours, the loop operates at very low temperature differentials. With the given load on the loop, this requires a high flow, and results in high pump energy!
Specifically, for a heat pump loop, I'm expecting a 7-10 F difference in supply and return temperatures at all times. I just ran a test model with a loop design DT specified at 10 F. For hours when there is a heating only load on the loop, I have an average difference in supply and return temperatures of about 3 degrees. This requires the pump to move about 3 times more water than necessary. My system is modeled with variable speed pumps, and isolation valves at each heat pump.
Any suggestions are greatly appreciated!