[Equest-users] PHOTOCELL-CTRL problem

B. Fountain bfountain at greensim.com
Fri Oct 23 13:03:53 PDT 2009


Nick,

Yes, you can edit the exterior lighting fractional schedule with the
photocell keywords.  You need to add this in the .inp -- it is not
currently in the eQUEST interface.

"Ext ltg sch" = SCHEDULE-PD
   TYPE             = FRACTION
   PHOTOCELL-CTRL   = DAY-OFF
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "ext ltg wk sch" )
   ..

Just tried it and it works great.

Brian


> I'm at the point of troubleshooting the application of PHOTOCELL-CTRL to
> my exterior lighting loads.
>
>
>
> My lighting loads are accounted under an electrical meter as shown on
> the attached image.
>
>
>
> The help file and previous discussions on this mailing list seem to
> indicate that the use of PHOTOCELL-CTRL requires that the referenced
> schedule be of the type "ON/OFF."
>
>
>
> The conflict is that a schedule applied to an exterior direct load under
> an electrical meter must be of the type "MULTIPLIER."  If I set up my
> schedules as "ON/OFF" per the PHOTOCELL-CTRL directions, they don't
> appear in the dropdown list to be selected in the attached screengrab.
>
>
>
> I want to apply PHOTOCELL-CTRL behavior for my exterior light
> schedules... can anyone point me in the right direction to make this
> happen?  Is it possible PHOTOCELL-CTRL just works when the schedule is
> of the type "MULTIPLIER?"
>
>
>
> Attached is the the DOE2 help file entry in its entirety for reference.
>
>
> Also for reference, my 3 Exterior Lighting Schedules look like this at
> the moment:
>
>
>
> ----------DAY
>
>
>
> "ExtLtg Dusk/Dawn DaySch" = DAY-SCHEDULE-PD
>
>    TYPE             = ON/OFF
>
>    VALUES           = ( 1, 1, 1, 1, 1, 1,
>
>                   1, 1, 1, 1, 1, 1,
>
>                   1, 1, 1, 1, 1, 1,
>
>                   1, 1, 1, 1, 1, 1 )
>
>    ..
>
> "ExtLtg Dusk/12AM DaySch" = DAY-SCHEDULE-PD
>
>    TYPE             = ON/OFF
>
>    VALUES           = ( 0, 0, 0, 0, 0, 0,
>
>                   0, 0, 1, 1, 1, 1,
>
>                   1, 1, 1, 1, 1, 1,
>
>                   1, 1, 1, 1, 1, 1 )
>
>    ..
>
> "ExtLtg Security DaySch" = DAY-SCHEDULE-PD
>
>    TYPE             = ON/OFF
>
>    VALUES           = ( 0, 0, 0, 0, 0, 0,
>
>                   0, 0, 0, 0, 0, 0,
>
>                   1, 0, 0, 0, 0, 0,
>
>                   0, 0, 0, 0, 0, 0, )
>
>    ..
>
>
>
> ----------WEEK
>
>
>
> "ExtLtg Dusk/Dawn WeekSch" = WEEK-SCHEDULE-PD
>
>    TYPE             = ON/OFF
>
>    DAY-SCHEDULES    = ( "ExtLtg Dusk/Dawn DaySch" )
>
>    ..
>
> "ExtLtg Dusk/12AM WeekSch" = WEEK-SCHEDULE-PD
>
>    TYPE             = ON/OFF
>
>    DAY-SCHEDULES    = ( "ExtLtg Dusk/12AM DaySch" )
>
>    ..
>
> "ExtLtg Security WeekSch" = WEEK-SCHEDULE-PD
>
>    TYPE             = ON/OFF
>
>    DAY-SCHEDULES    = ( "ExtLtg Security DaySch" )
>
>    ..
>
>
>
> ----------ANNUAL
>
>
>
> "ExtLtg Dusk/Dawn AnnSch" = SCHEDULE-PD
>
>    TYPE               = ON/OFF
>
>    PHOTOCELL-CTRL     = DAY-OFF
>
>    MONTH              = ( 12 )
>
>    DAY                = ( 31 )
>
>    WEEK-SCHEDULES     = ( "ExtLtg Dusk/Dawn WeekSch" )
>
>    ..
>
> "ExtLtg Dusk/12AM AnnSch" = SCHEDULE-PD
>
>    TYPE               = ON/OFF
>
>    PHOTOCELL-CTRL     = DAY-OFF
>
>    MONTH              = ( 12 )
>
>    DAY                = ( 31 )
>
>    WEEK-SCHEDULES     = ( "ExtLtg Dusk/12AM WeekSch" )
>
>    ..
>
> "ExtLtg Security AnnSch" = SCHEDULE-PD
>
>    TYPE               = ON/OFF
>
>    MONTH              = ( 12 )
>
>    DAY                = ( 31 )
>
>    WEEK-SCHEDULES     = ( "ExtLtg Security WeekSch" )
>
>
>
>
>
>
>
> NICK CATON, E.I.T.
>
> PROJECT ENGINEER
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> Check out our new web-site @ www.smithboucher.com
>
>
>
> From: Brian Fountain [mailto:bfountain at greensim.com]
> Sent: Friday, July 10, 2009 9:12 PM
> To: Nick Caton
> Cc: equest-users at lists.onebuilding.org
> Subject: Re: [Equest-users] Editing External lighting Schedule
>
>
>
> You mean something like this (from the new features help file)...
>
>
> PHOTOCELL-CTRL
>
>
> Accepts a code-word specifying whether the hourly value in the
> referenced DAY-SCHEDULE can be overridden either ON (value = 1.0) or OFF
> ( value = 0.0) according to whether it is day or night.
>
> DAY-OFF                     Forces the hourly schedule value to be 0.0
> whenever the sun is up.
>
> DAY-ON                       Forces the hourly schedule value to be 1.0
> whenever the sun is up.
>
> NIGHT-OFF                  Forces the hourly schedule value to be 0.0
> whenver the sun is down.
>
> NIGHT-ON                   Forces the hourly schedule value to be 1.0
> whenever the sun is down.
>
> For example, assume lighting in a parking lot is to be on from dusk
> until 11 p.m. The earliest the lights are allowed to illuminate is 4
> p.m., but will not actually start until the sun is down:
>
> "Parking Lot DSch" = DAY-SCHEDULE-PD
> TYPE               = ON/OFF
> VALUES             = ( 0., 0., 0., 0., 0., 0.,
>                        0., 0., 0., 0., 0., 0.,
>                        0., 0., 0., 1., 1., 1.,
>                        1., 1., 1., 1., 1., 0. )
>
> "Parking Lot WSch" = WEEK-SCHEDULE-PD
> TYPE               = ON/OFF
> DAY-SCHEDULES      = ("Parking Lot DSch")
> ..
>
> "Parking Lot Sch" = SCHEDULE-PD
> TYPE               = ON/OFF
> PHOTOCELL-CTRL     = DAY-OFF
> MONTH              = (12)
> DAY                = (31)
> WEEK-SCHEDULES     = ("Parking Lot WSch")
> ..
>
>
>
>
>
>
> Nick Caton wrote:
>
> With regard to exterior lighting, It occurred to me today that eQuest
> currently has the capability to determine the operating hours of
> interior lights based on an amount of daylight, specific to the hours of
> daylight occurring during the year for a given location, using the
> daylighting functions...
>
> How much of a stretch/challenge would it be to accurately determine how
> often photocell-controlled exterior lights are operating through the
> year based on available daylight outside of the building??
>
> It might be an awesome feature to consider for future wizards: where one
> simply defines the exterior lighting wattage, and could additionally
> designates realistic timeclock/photocell controls, such as "on when it
> turns dark and off after 2AM."
>
> NICK CATON, E.I.T.
> PROJECT ENGINEER
> 25501 west valley parkway
> olathe ks 66061
> direct 913 344.0036
> fax 913 345.0617
> Check out our new web-site @ www.smithboucher.com
>
> -----Original Message-----
> From: equest-users-bounces at lists.onebuilding.org [
> mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
> Matutinovic, Luka
> Sent: Friday, July 10, 2009 9:03 AM
> To: John Aulbach; equest-users at lists.onebuilding.org; nate murray
> Subject: Re: [Equest-users] Editing External lighting Schedule
>
> I had limited success in editing the Wizard schedules by adjusting the
> max and min thresholds on the vertical axis and the start and end hours
> along the top axis.  My understanding is that eQuest generates those
> schedules based on the building type definition at the beginning of the
> shell wizard.  I had many headaches trying to edit the schedule after I
> realized I selected the wrong building type, especially when dealing
> with multiple shells. I inevitably end up using John's approach once in
> the detailed mode.
>
> When people are creating models for LEED, do you use the schedules found
> in the back of the 90.1 User's Manual, or do you create your own
> schedules?  How has the USGBC reviewed this issue since according to App
> G, schedule creation is up to the designer and the "rating authority"?
> It would seem to me that the USGBC wouldn't care as long as you use
> schedules that are reasonable for the building type and anticipated
> operation, and that the reference building uses the same ones (unless
> daylight controls or demand controlled ventilation is being dealt with
> through schedules and not simulation software directly).
>
> Any thoughts?
>
> Thanks,
> Luka Matutinovic
>
> -----Original Message-----
> From: equest-users-bounces at lists.onebuilding.org [
> mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John
> Aulbach
> Sent: Friday, July 10, 2009 1:47 AM
> To: equest-users at lists.onebuilding.org; nate murray
> Subject: Re: [Equest-users] Editing External lighting Schedule
>
>
> Nate:
>
> The only way I know to edit such schedules is to change the mode to
> Detailed Edit, then make the schedule changes.
>
> If you try to go back to the Wizard mode, those changes will be deleted.
>
> John Aulbach
>
> --- On Thu, 7/9/09, nate murray <natemurr at gmail.com>
> <mailto:natemurr at gmail.com>  wrote:
>
>
>
> 	From: nate murray <natemurr at gmail.com>
> <mailto:natemurr at gmail.com>
> 	Subject: [Equest-users] Editing External lighting Schedule
> 	To: equest-users at lists.onebuilding.org
> 	Date: Thursday, July 9, 2009, 5:59 PM
> 	Hi,
> 	I want to make the external lighting schedule so that there is a
>
> 	little bit smaller loads in april and october then the rest of
> the
> 	months. I see the monthly profiles on the External lighting
> screen in
> 	Design Wizard, but how do I go about editing those monthly
> 	profiles...if that's what I should do.
>
>
> 	Thanks,
> 	--
> 	Nathan Murray
>
>
>
> 	-----Inline Attachment Follows-----
>
> 	_______________________________________________
> 	Equest-users mailing list
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> 	To unsubscribe from this mailing list send  a blank message to
> 	EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
>





More information about the Equest-users mailing list