[Equest-users] Would cheaper fuel be credited?
Rob Rosen
rrosen at taitem.com
Tue Sep 8 09:57:15 PDT 2009
ASHRAE Appendix G Modeling Guidelines Tables 3.1.1A and 3.1.1B give the
baseline HVAC system for each type of building. The baseline heating fuel in
all cases is either fossil fuel or electricity. I believe that a different
fuel may be used in the proposed building, if it is a purchased, renewable
fuel (such as wood pellets).
Appendix G Section 2.4 Exception says that if the renewable fuel is
site-generated or free (such as burning waste wood from packing crates),
then it cannot be modeled as a proposed fuel for the purpose of calculating
building performance.
Rob Rosen
Senior Energy Analyst
Taitem Engineering
110 S. Albany St.
Ithaca, NY 14850
Phone: 607-277-1118 ext 110
Fax: 607-277-2119
_____
From: YinRic [mailto:cesseric at hotmail.com]
Sent: Monday, September 07, 2009 2:18 AM
To: Equest User
Subject: [Equest-users] Would cheaper fuel be credited?
Hi Users,
In a project, the client wants to use a cheap local fuel (bamboo pellet,
rapidly renewable) to reduce annual energy cost and score high on EAc1. I am
wondering if in baseline, the fuel must also be bamboo pellet or could be
something else, say, natural gas, the price of which is higher per thermal
unit? I do not seem to find where in ASHRAE 90.1-2004 dictates that in
baseline and proposed, the fuel must be the same. Any comments are
appreciated.
Thanks,
Rick, PE, LEED AP
_____
搜索本应是快乐的,不是么? 快乐搜索,有问必应!微软隆重推出! 立即试用!
<http://bing.com.cn?FORM=M00HCN&Publ=WLHMTAG&Crea=TEXT_Search_Where_You_Are_
1X1>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090908/eff3144a/attachment-0001.htm>
More information about the Equest-users
mailing list