[Equest-users] SUPPLY-KW/FLOW
Vikram Sami
VSami at lasarchitect.com
Thu Sep 17 12:19:38 PDT 2009
Yes, but I think it refers to kW/cfm
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
From: Brett Fero [mailto:bfero at robsonwoese.com]
Sent: Thursday, September 17, 2009 3:08 PM
To: Vikram Sami; Lars Fetzek; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] SUPPLY-KW/FLOW
How about this:
9.9 BHP (output)/0.93 eff = 10.645 hp (input)
10.645 hp input x 0.7457 kW/hp = 7.94 kW
Brett Fero, P.E., LEED AP
RobsonWoese Inc.
Salina Meadows Office Park
301 Plainfield Road, Suite 180
Syracuse, NY 13212
Phone: 315-445-2650
Fax: 315-445-0958
bfero at robsonwoese.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vikram
Sami
Sent: Thursday, September 17, 2009 2:40 PM
To: Lars Fetzek; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] SUPPLY-KW/FLOW
Maybe I'm mistaken here, but I've always understood the Supply flow to
be kW/cfm. So if your design condition is 9.9 BHP, what is the design
flow rate (in cfm) that goes with that?
So for instance if your design flow rate is 20,000 cfm at 9.90 BHP, then
your Supply KW/Flow = 12.83/20,000 = 0.000642
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Lars
Fetzek
Sent: Wednesday, September 16, 2009 4:48 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] SUPPLY-KW/FLOW
eQuesters & DOE2-2ers,
The DOE2-2 dictionary loves to use the phrase, "total fan power per
unit flow" in defining SUPPLY-KW/FLOW. Clear as mud.
I figured this: At design conditions, the supply fan runs at 9.90
BHP and 61.89% efficiency and the per-unit flow is at unity ( x CFM / x
CFM = 1). The motor nominal efficiency is 93%. (No, I don't have a
motor efficiency curve.) 0.746 kW = 1 HP. Therefore, the fan kW =
9.90 * 0.746 / ( 0.6189 * 0.93 ) = 12.83 kW. The per unit flow is 1.
So... SUPPLY-KW/FLOW = 12.83, which I type into my .inp file.
Naturally, eQuest gives me an error message, insisting that
SUPPLY-KW/FLOW must be between 0.0 and .0080. Evidently, there is some
discrepancy involving units or the meaning of "per unit" in the context
of the quoted phrase.
Can anyone clarify what eQuest really means and how to calculate
SUPPLY-KW/FLOW? Is it supposed to be KW-per-CFM?
Thanks!
Lars Fetzek, EI
Phoenix Engineering Group
Tampa, Florida
________________________________________________________________________
This Email has been scanned for all viruses by PAETEC Email Scanning
Services, utilizing MessageLabs proprietary SkyScan infrastructure. For
more information on a proactive anti-virus service working around the
clock, around the globe, visit http://www.paetec.com.
________________________________________________________________________
________________________________
"This message is for the designated recipient only and may contain
privileged, proprietary, or otherwise private information. If you are
not the intended recipient, you are hereby notified that any disclosure,
copying, distribution, or the taking of any action in reliance on the
contents of this information is strictly prohibited. If you have
received this transmission in error, please notify the sender
immediately by e-mail and delete the original message."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090917/57271bf9/attachment-0002.htm>
More information about the Equest-users
mailing list