[Equest-users] Heat Pump Supplemental Heat
Carol Gardner
cmg750 at gmail.com
Thu Apr 22 11:45:41 PDT 2010
Michael,
Try this:
Under Air-Side System HVAC Parameter, Supp Heat/Defrost, try entering a
really low number for the HP Supp Heat Capacity, on the order of .001 Btuh
or so.
Carol
On Thu, Apr 22, 2010 at 7:58 AM, M. Shields <mshields at fstrategies.com>wrote:
> Fellow eQuesters,
>
>
>
> I am trying to model a building using heat pumps, however, there will be no
> backup heaters in the building. Is there a way to disable this from the
> model? When I ran the wizard I selected the heating source was “DX Coils
> (Heat Pump)” but when I go through the reports there is consumption for “HT
> Pump Supplem”.
>
>
>
> Thanks,
>
> Michael
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100422/001944d5/attachment-0001.htm>
More information about the Equest-users
mailing list