[Equest-users] How to turn off hot water loop and how to make aFCU+DOAS system simulation

Kelsey VanTassel KVanTassel at sustaineng.com
Wed Apr 21 06:47:30 PDT 2010


This is easy to fix. You cannot assign systems directly to spaces, they must be associated with a thermal zone. Under “airside HVAC” right click on project and choose “create thermal zone.” Assign the dummy zone to the dummy space and then assign the system to the zone (double click on the zone, under “basic specifications” set the parent system to DOAS).

Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com<mailto:kvantassel at sustaineng.com>

[cid:image001.jpg at 01CAE12E.F20612F0]

We've moved. Please see below for my new contact info.

901 Deming Way, Ste. 201
Madison, WI 53717
608.836.4488 ext. 20| Fax: 608.836.4477

2009 Dane County Small Business Award Recipient

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of tsea2005
Sent: Tuesday, April 20, 2010 8:34 PM
To: Rob Hudson
Cc: equest-users at lists.onebuilding.org; JGrando
Subject: Re: [Equest-users] How to turn off hot water loop and how to make aFCU+DOAS system simulation

Hi Rob Hudson,
                 First thanks for your reply. I followed you advice that set the snap temp to 120, and there is no heating load, I made it .
                  But for the DOAS system ,as you said that the dummy space doesn't need to have walls or loads,I created a new floor named dummy floor using a box with 1ft width ,1ft depth and 1ft floor-floor.Then in the dummy floor ,I created a child space named dummy space with box-shaped,1ft width ,1ft depth. After this ,I created a new HVAC system named DOAS system , that is SZRH.Here is the problem:the DOAS system's "control zone" dose't include the dummy space defined ealier,as the chart showed below, So I have to cancel.
[cid:image003.jpg at 01CAE12E.F20612F0]
2010-04-20
________________________________
The simulation can't run ,then I checked the building description,it turned out as the chart showed below:
 [cid:image005.jpg at 01CAE12E.F20612F0]
I do know that I have misunderstood the method definfying the dummy space ,what is the correct one?I’ve attached my INP and PD2 files.


2010-04-21
________________________________
tsea2005
________________________________
发件人: Rob Hudson
发送时间: 2010-04-19  22:07:20
收件人: Grando, John
抄送: tsea2005; equest-users at lists.onebuilding.org
主题: Re: [Equest-users] How to turn off hot water loop and how to make aFCU+DOAS system simulation
you can keep the heating and hot water in the model, and simply use "non heating" thermostat schedules that will allow the space to be satisfied without turning on the hot water coils.  also in the hot water loop there is a snap temperature.  set this to 120 or something high and the boilers and attached equipment will never turn on.

also for the DOAS system with FCU equipment.  i have done exactly that and gotten good results.  Start by setting all your FCU systems to have OA-FROM-SYSTEM to the DOAS system and make sure that the DOAS system is attached to a "dummy space."  this space doesn't need to have walls or loads, just 1sqft of space and the correct thermostat schedules and it should work just fine.
2010/4/19 Grando, John <JGrando at cosentini.com<mailto:JGrando at cosentini.com>>
You can just select it as it is and then remove it in Detailed edit or set the heating level to something extremely low (55F).


John Grando LEED AP| Mechanical Engineer




________________________________
From: tsea2005 [mailto:tsea2005 at 163.com<mailto:tsea2005 at 163.com>]
Sent: Saturday, April 17, 2010 2:56 AM

To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] How to turn off hot water loop and how to make a FCU+DOAS system simulation

Hi all:
       I am simulating a building which dosen't need heating via FCU,but in eQuest's air-side system,there is the  4-pipe Fan coils with HW heat. [cid:__2 at Foxmail.net]  I don't need heating so how can i turn off the heat water loop in detailed interface mode?

     Another question is HOw to service the whole building with both FCU and DOAS?

Thank you so much!
2010-04-17
________________________________
tsea2005

NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof. In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law. If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission. Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege. If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>



--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100421/72462fe8/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 31773 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100421/72462fe8/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 19069 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100421/72462fe8/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 26430 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100421/72462fe8/attachment-0008.jpg>


More information about the Equest-users mailing list