I found that tab and have been playing around with it. I switched the
source on all of my heat pumps to "Not Installed" but I'm still getting some
supplemental energy use (although it is relatively small). Thanks for the
tip!
Michael
From: Carol Gardner [mailto:cmg750 at gmail.com]
Sent: Thursday, April 22, 2010 2:46 PM
To: M. Shields
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Heat Pump Supplemental Heat
Michael,
Try this:
Under Air-Side System HVAC Parameter, Supp Heat/Defrost, try entering a
really low number for the HP Supp Heat Capacity, on the order of .001 Btuh
or so.
Carol
On Thu, Apr 22, 2010 at 7:58 AM, M. Shields <mshields at fstrategies.com>
wrote:
Fellow eQuesters,
I am trying to model a building using heat pumps, however, there will be no
backup heaters in the building. Is there a way to disable this from the
model? When I ran the wizard I selected the heating source was "DX Coils
(Heat Pump)" but when I go through the reports there is consumption for "HT
Pump Supplem".
Thanks,
Michael
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100422/612e1667/attachment-0002.htm>
More information about the Equest-users
mailing list