[Equest-users] WSHP COP penalty
Adam.Boyd at CH2M.com
Adam.Boyd at CH2M.com
Fri Apr 30 08:31:38 PDT 2010
Rebecca, one sanity check on that number is that the increase in natural gas energy should be about equivalent to the electrical energy saved on the compressors for heating due to the increase COP. If there is a lot of simultaneous heating and cooling going on, the penalty might be even larger since your cooling units are rejecting less heat to the loop. That should give you an idea if something fishy is going on.
Adam
From: Nicholas Couture, LEED AP [mailto:ncouture at emtec-engineers.com]
Sent: Friday, April 30, 2010 6:48 AM
To: Shea, Rebecca; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] WSHP COP penalty
Rebecca,
If the COP is getting better as you mention 2.9 to 4.5, wouldn't you be saving heating electricity rather than getting a penalty?
Nick Couture, LEED AP
Mechanical Engineer
[cid:image001.jpg at 01CAE83F.8D5FCD10]
3555 Veteran's Memorial Highway, Suite M
Ronkonkoma, NY 11779
Tel: 631.981.3990 ext. 230
Fax: 631.981.3971
ncouture at emtec-engineers.com
www.emtec-engineers.com <http://www.emtec-engineers.com/>
This message is intended only for the personal and confidential use of the designated recipient(s) named above. This is not in anyway an official statement of Emtec Consultants or solicitation to buy our services. Emtec Consultants does not guarantee this Email transmission to be secure or error-free. Any reproduction or changes to our drawings and files without the consent of Emtec Consultants is strictly prohibited.
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Shea, Rebecca
Sent: Friday, April 30, 2010 9:19 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] WSHP COP penalty
We're replacing 125 WSHPs at a building that are about 15 years old. The EER is going from about 8.5 to 15, and the COP is going from 2.9 to 4.5. I would expect electric savings and a slight heating penalty for the increase in COP, but I'm getting -20% heating penalty. Any help is appreciated...
-Beka
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100430/65be4771/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 26315 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100430/65be4771/attachment-0002.jpg>
More information about the Equest-users
mailing list