[Equest-users] [eQuest-users] Transformers in Energy Model
Nick Caton
ncaton at smithboucher.com
Mon Aug 16 14:53:34 PDT 2010
First, thanks to Jason for the heads up! Taking credit for premium
efficiency transformers is a pretty novel idea in my circles.
I'm re-directing this response/discussion to eQuest-users as I'm
applying this in eQuest and have found a snag along the way...
After coming up with and creating a custom TRANS-LOSS-FPLR curve using
manufacturer data, I hop over to create a new meter to assign this to.
The default transformer size field starts off blank, as transformer
losses are not normally modeled. After entering the transformer size
(225kVA) on the first screen, I immediately encounter the following
dialog:
[text includes: "Range Checking Violation: Value must be > 1"]
Hmm. This seems odd... the text files for TRANSFORMER-LOSS and
TRANS-LOSS-FPLR both indicate this value should be a fraction of the
Transformer size representing the maximum loss (therefore < 1). In my
example, the 225kVA transformer has a maximum loss (at full load) of
3,898VA, so I was expecting TRANSFOMER-LOSS should be 3898/225000 =
0.01732. Regardless, I haven't entered anything in that field yet... so
clicking Cancel to proceed, I return to the following:
Hmm.
The error appears to result from the "Loss:" field being unpopulated. I
cannot however input the Loss ratio (clouded "n/a") for the custom curve
to be applied against! The field ignores anything I type when
highlighted...
Okay so saving and exiting, I navigate the .inp to add TRANSFORMER-LOSS
there:
"Step Down Meter" = ELEC-METER
TYPE = BUILDING
TRANSFORMER-SIZE = 225
TRANSFORMER-LOSS = .01732
TRANS-LOSS-FPLR = "Custom Xfrmr fPLR"
..
Starting eQuest back up, the following error is generated in BDL -
(eQuest proceeds to open and overwrite .01732 with a zero):
*13249* "Step Down Meter" = ELEC-METER
*13250* TYPE = BUILDING
*13251* TRANSFORMER-SIZE = 225
*13252* TRANSFORMER-LOSS = .01732
*ERROR**************************** ======
****************************************************
*ERROR*****VALUE NOT BETWEEN 1.0000 AND 1.5000
*13253* TRANS-LOSS-FPLR = "Custom Xfrmr fPLR"
Here's where I throw up my hands! What interpretation of
TRANSFORMER-LOSS results in a value that would always fall between 1.0
and 1.5?
On a related note: I've read through all the help files regarding
electrical meters (I think)... Once this is meter up and running, can
anyone suggest any method for applying a specific subset of electric
loads (say, only plug loads) to this new meter with the transformer
losses defined?
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sami,
Vikram
Sent: Wednesday, August 11, 2010 4:00 PM
To: Sami, Vikram; Jason Boehning; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Transformers in Energy Model
I should have mentioned I was referring to eQUEST...
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com
www.perkinswill.com <http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sami,
Vikram
Sent: Wednesday, August 11, 2010 4:31 PM
To: Jason Boehning; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Transformers in Energy Model
You can model transformer sizes and losses in the detailed edit mode
when you open up you electric meter.
I have to confess I have not modeled a transformer in a model yet (the
default is not to model a transformer and the loss associated). You can
specify a loss part load curve too:
TRANS-LOSS-FPLR
Takes the U-name of a curve that gives the multiplier on
TRANSFORMER-LOSS as a function of the part load ratio (current hour load
on the meter divided by TRANSFORMER-SIZE). The transformer loss is
calculated hourly as
(TRANSFORMER-SIZE) x (TRANSFORMER-LOSS) x (TRANS-LOSS-FPLR
value)
The load is the sum of that due to all directly connected equipment and,
for TYPE = UTILITY and BUILDING, other ELEC-METERs. The default curve is
linear from 0.1 at zero load to 1.0 at full load.
Like I said I haven't done it yet - good luck. Let me know how it turns
out
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com
www.perkinswill.com <http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jason
Boehning
Sent: Wednesday, August 11, 2010 4:14 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Transformers in Energy Model
I am new to energy modeling and I am curious if there is a way to take
credit for more efficient transformers in an energy model. Some of our
transformer reps have said that there is not a LEED credit for more
efficient transformers, but you have to gain the credit through the
energy model. Would it just be through more heat in a space? I
appreciate any information I can get in this matter.
Best Regards,
Jason Boehning, EIT
Mechanical Engineer
6161 Savoy, Suite 1212
Houston, Texas 77036
v. 713.482.2322
f. 713.482.2314
e. Jason.Boehning at ricegardner.com
<mailto:Jason.Boehning at ricegardner.com>
This email and any files transmitted with it are confidential and
intended solely for the addressee. If you are not the named addressee
you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100816/10e12f8d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100816/10e12f8d/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 3662 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100816/10e12f8d/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 9972 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100816/10e12f8d/attachment.png>