[Equest-users] (eQuest Users) Summer heating in a VAV system
Carol Gardner
cmg750 at gmail.com
Wed Aug 18 07:53:28 PDT 2010
Hi Scott,
I would look through the load part of your model for the answer. For
instance I notice that many of you spaces have no equipment loads, including
your mechanical room (!?!). Put a small w/sf in each space. Your occupancy
loads are also small compared to what other building types have. Also, look
at your schedules to see if you agree with the default. After that if you
are still having a problem, let us know.
Best,
Carol
On Wed, Aug 18, 2010 at 7:37 AM, Tomlinson, Scott <stomlinson at smma.com>wrote:
> Folks,
>
>
>
> I am having issues with VAV systems in eQuest. This is a reoccurring
> problem for me. I am getting large amounts of heating during the summer. I
> suspect this is due to reheat at the VAV terminals. I’ve tried everything I
> can think of to eliminate this. I have lowered my minimum VAV flow rates,
> lowered my summer heating setpoint temp to 55, locked out my boilers based
> on higher outside air temps. All these changes eliminated my summer
> heating. But they also shot my unmet heating hours way up. Does anyone have
> any other suggestions on how to correct this?
>
>
>
> Thank you,
>
> __________________________________________
>
> *Scott Tomlinson, PE, LEED-AP*
>
> Mechanical
>
> *Symmes Maini & McKee Associates, Inc.*
>
> 1000 Massachusetts Avenue, Cambridge, MA 02138
>
> t: 617.520.9438
>
> [image: http://intranet/Images/USGBC.jpg]
>
>
>
> f: 617.354.5758
>
> stomlinson at smma.com <STomlinson at smma.com>
>
> www.smma.com
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100818/54961f18/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14792 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100818/54961f18/attachment-0001.jpeg>
More information about the Equest-users
mailing list