[Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*
Carol Gardner
cmg750 at gmail.com
Thu Aug 26 15:13:25 PDT 2010
If you have an economizer you had better put the econo-low-limit temperature
in. It is necessary. You can access help screens in DD edit also. Once again
I encourage you to read the on line help using the pull down menu. I do
believe econo-low-limit temp is available in the wizards too.
On Thu, Aug 26, 2010 at 12:37 PM, Adrian Gurga <gurga at illinois.edu> wrote:
> Chris,
>
> I understand. For some reason it appears that the wizards will sometimes
> generates a DOE2 input which doesn't include the econo-low-limit line and
> thereby generates a warning. I'm not sure what causes this to happen, but as
> long as the model runs without it, I won't bother. Thanks for direction to
> the DOE2 definitions file, that's the one I was looking for. It describes in
> detail what econo-low-limit is used for and it probably isn't relevant to my
> purposes. I think we can call this case closed.
>
> On Thu, Aug 26, 2010 at 2:00 PM, Otto Schwieterman <oschwieterman at fhai.com
> > wrote:
>
>> I would tweak it in the detailed edit mode because it is very unlikely
>> that you can get good results by simply using the wizard. There are too many
>> major variables that you cannot change in the wizard. You might as well pick
>> the cost/energy consumption via experience if you are not going to go into
>> the detailed edit mode.
>>
>>
>>
>> If you simply need eQUEST to spit something out so you have results to
>> show I would ignore the econo-low-limit but remember that the results mean
>> nothing.
>>
>>
>>
>> *From:* Adrian Gurga [mailto:gurga at illinois.edu]
>> *Sent:* Thursday, August 26, 2010 1:38 PM
>> *To:* James Hansen
>> *Cc:* equest-users at lists.onebuilding.org
>>
>> *Subject:* Re: [Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*
>>
>>
>>
>> Excellent. Thanks James. And yes, it's up to us to figure out how to use
>> it, which I think qualifies as "no support". I'm sure the programmers
>> responsible for the software are perfectly competent, and I did not mean to
>> suggest otherwise. I suppose what I really meant to say was that the
>> software has no customer support, which is understandable because it's free.
>>
>>
>>
>>
>> Now back to the model. So one would have to go into the detailed mode in
>> order to change this parameter? If one was to work with a model only via
>> the DD wizard as we sometimes do for order of magnitude estimates, would it
>> be OK to leave ecnono-low-limit unused? or would this result in inaccurate
>> results?
>>
>> On Thu, Aug 26, 2010 at 12:22 PM, James Hansen <JHANSEN at ghtltd.com>
>> wrote:
>>
>> See below. Also, the technical support isn’t “very poor”, it’s just that
>> the people working on technical issues are actually programmers. It’s up to
>> us to figure out how to use it properly.
>>
>>
>>
>>
>>
>> *GHT Limited
>> **James Hansen, PE, LEED AP*
>>
>> *Senior Associate*
>>
>> 1010 N. Glebe Rd, Suite 200
>>
>> Arlington, VA 22201-4749
>>
>> 703-338-5754 (Cell)
>>
>> 703-243-1200 (Office)
>>
>> 703-276-1376 (Fax)
>>
>> www.ghtltd.com
>>
>> * *
>>
>>
>>
>> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
>> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Adrian Gurga
>> *Sent:* Thursday, August 26, 2010 1:13 PM
>>
>>
>> *To:* equest-users at lists.onebuilding.org
>> *Subject:* Re: [Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*
>>
>>
>>
>> Carol,
>>
>>
>>
>> With all due respect, "Only to input the temperature and to look at your
>> help screen." is not a complete sentence. Please reply using English if
>> you'd like to post on a listserv. If you have advice on how to address this
>> warning, please provide it. Additionally, "Flaming" (
>> http://www.urbandictionary.com/define.php?term=flaming) is a behavior
>> typically reserved for prepubescents on chat forums, not professional
>> listservs. Please show some professional courtesy in your responses. Now,
>> let's move forward amicably and discuss the actual topic of the post.
>>
>>
>>
>> All,
>>
>>
>>
>> We all know that as eQUEST is free software, it has very poor technical
>> support which is why listservs like this exist. Here is the research I've
>> done so far. Inputting a seach for "econo-low-limit" or even just "econo"
>> in the eQUEST helpfile produces no results. Are there "pull down help
>> menus" which discuss this topic as Carol suggests? If so, please direct me
>> to them. Googling "econo-low-limit" produces one relevent hit other than
>> this listserv, a user poses the same question I have, but is issue is never
>> resolved (http://www.energymodelhelp.com/SMF/index.php?topic=107.0 ). A
>> search of "econo-low-limit" on this listserv will yield five results. In
>> four of these, "econo-low-limit" is simply listed as an input, in the fifth,
>> it is suggested as a way of manipulating the model. However, I cannot find
>> anywhere on this listserv where the warning "econo-low-limit" = unused has
>> been discussed. Therefore, I assume it's a reasonable to post and and I
>> hope it will be helpful to future users.
>>
>>
>>
>> I can't figure out where to specify an econo-low-limit in the DD wizard,
>> if I need to go into the detailed edit to address this, please let me know
>> where that variable is edited. I have attempted to edit the files manually
>> in notepad to specify an econo-low-limit, so far have had no luck, but
>> truthfully I'm not too experienced with manual edits. If anyone could
>> provide some assistance with where to edit this parameter, it would be
>> appreciated. Alternatively, if this warning does not have detrimental
>> impact on the outputs, I will just ignore it.
>>
>>
>>
>> Thanks for your thoughts and comments.
>>
>>
>>
>> --
>> Adrian Gurga
>> Smart Energy Design Assistance Center
>> University of Illinois - Urbana-Champaign
>> www.sedac.org
>> (217) 244-4671
>> (800) 214-7954
>>
>>
>>
>> On Thu, Aug 26, 2010 at 11:08 AM, Carol Gardner <cmg750 at gmail.com> wrote:
>>
>> That was polite, Jason. Users of this list need to be responsible enough
>> to at least look at the pull down help menus before asking a question on the
>> listserv, It is impolite and wasteful of everyone's time to not do so. I
>> have sympathy for someone who is learning but if they really care to learn
>> this skill and be in the business they need to learn to at least try to find
>> the answers they need. Perhaps the college systems have changed, which would
>> be a shame, but when I was in school I had to research and find my own
>> answers. Since I'm older than dirt we didn't have listservs, Google, or any
>> of those useful tools that now make finding answers so much easier.
>>
>> I rest my case,
>>
>> Carol
>>
>>
>>
>> On Thu, Aug 26, 2010 at 8:11 AM, Jason Glazer <jglazer at gard.com> wrote:
>>
>> Carol,
>>
>> The eQUEST-user mailing list is for users of all experience levels:
>>
>> "The eQUEST-users mailing list is for everyone that uses the eQUEST
>> program. Users at every experience level are encouraged to join this mailing
>> list and share their questions and knowledge. Users of the DOE-2.2 and
>> D2Comply are also welcome. The mailing list will be a user-to-user support
>> forum for eQUEST, DOE-2.2, and D2Comply."
>>
>> We appreciate your contribution but please either reply politely or not at
>> all.
>>
>> Jason
>>
>>
>>
>> On 8/26/2010 9:29 AM, Carol Gardner wrote:
>>
>> Only to input the temperature and to look at your help screen. This is
>> something you really should be able to figure out yourself. If you can't
>> try another profession.
>>
>> Carol
>>
>> On Tue, Aug 24, 2010 at 11:55 AM, Adrian Gurga <gurga at illinois.edu
>>
>> <mailto:gurga at illinois.edu>> wrote:
>>
>> I am working with a model and am working with the following warning
>> whenever it runs the BDL Load File Log
>>
>> Line 1336: Warning Encountered:
>> INPUT-TYPE COEFFICIENTS ..
>> ECONO-LOW-LIMIT = *UNUSED*
>>
>> Any ideas?
>>
>> --
>> Adrian Gurga
>> Smart Energy Design Assistance Center
>> University of Illinois - Urbana-Champaign
>>
>> www.sedac.org <http://www.sedac.org/>
>>
>>
>> (217) 244-4671
>> (800) 214-7954
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>>
>>
>>
>>
>>
>>
>> --
>> Carol Gardner PE
>>
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>> --
>> Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
>> Admin for onebuilding.org building performance mailing lists
>>
>>
>>
>> --
>> Carol Gardner PE
>>
>>
>>
>> ------------------------------
>>
>> The information contained in this communication is confidential, may be
>> privileged, and is intended only for the use of the addressee. It is the
>> property of GHT Limited. Unauthorized use, disclosure or copying of this
>> communication or any part thereof is strictly prohibited and may be
>> unlawful. If you have received this communication in error, please notify
>> me immediately by return e-mail or by e-mail to ght at ghtltd.com, and
>> destroy this communication and all copies thereof, including all
>> attachments. Thank you.
>>
>>
>>
>>
>> --
>> Adrian Gurga
>> Smart Energy Design Assistance Center
>> University of Illinois - Urbana-Champaign
>> www.sedac.org
>> (217) 244-4671
>> (800) 214-7954
>>
>> ________________________________________________________________________________________
>> Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
>> designated individual or entity. If you received this message in error, please notify the sender by replying
>> to the electronic mail (if electronic) or by telephone at the number indicated on this document.
>> Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
>> electronic mail. Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
>> from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
>> of this message by unintended recipients is not authorized and maybe unlawful. Any information included in
>> this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
>> Associates, Inc. may not be covered by our professional liability insurance.
>>
>>
>>
>
>
> --
> Adrian Gurga
> Smart Energy Design Assistance Center
> University of Illinois - Urbana-Champaign
> www.sedac.org
> (217) 244-4671
> (800) 214-7954
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100826/ed290a7d/attachment-0005.htm>
More information about the Equest-users
mailing list