[Equest-users] Equest v 3.63 - Pkg Heat Pump - heating output
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Aug 19 06:30:51 PDT 2010
Mike,
As a new user, you should use the built-in help menu in most entry
fields by right-clicking and selecting "Item Help".
After that, check the equest-users archives here:
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/
The "nan" is discussed in a thread here:
http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010
-February/003189.html
Sounds like you have a loop flow that is way out of range (perhaps too
high or zero). If you entered any capacities manually, keep in mind that
"MBtu/h" for the capacity field means millions, not thousands of Btu/h.
If you still can't figure it out, attach your eQUEST project file and
input (.inp) file to a subsequent post.
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mike
Schaefer
Sent: Thursday, August 19, 2010 9:13 AM
To: EQuest
Subject: [Equest-users] Equest v 3.63 - Pkg Heat Pump - heating output
While modeling a variable speed blower fan and variable compressor
rooftop unit heat pump the Simulation Report lists the EM1 Electricity
MBTU for space heating as "nan". Does anyone know why I don't receive a
quantity for heating?
Also when comparing the VAV blower fan Heat Pump (with digital scroll
compressor) design with a CV blower fan Heat Pump (Single Stage
Compressor) design I only recieve a partial savings in cooling.
I've attached my files for both a CV and VAV volume Heat Pump.
BTW: this is my first time using this software.
Michael Schaefer - P.E., LEED(r) AP
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100819/0cc49806/attachment-0002.htm>
More information about the Equest-users
mailing list