Hello!

For Climate Zone 5, IECC requires a minimum insulation value of R-13 + R-7.5 c.i. for a steel framed building. If the studs are 16" on center, the thermal bridging degrades the batt R-value of 13 down to an effective R-6 c.i. which bring the total insulation value to R-13.5 c.i. Currently, I am reviewing a building with 2.5" of R-5 extruded polystyrene total an insulation value of R-12.5 c.i. However, the building wall assembly exceeds the 'Assembly Minimum' of U-value 0.064. Since IECC 2009 is the effective energy code of Massachusetts since June 30, 2010, is the insulation assembly in agreement with the Minimum Envelope Requirements if the 'Assembly Maximum' is exceeded? Any input will be much appreciated!