[Equest-users] equest crashing on chilled water loop primaryselection
Shaun Martin
smartin at shaunmartinconsulting.com
Wed Dec 15 15:12:00 PST 2010
You only seem to have a chilled water meter attached to this loop - no
primary equipment (chiller) so there is nothing to size to.
Shaun Martin LEED AP
Principal
Shaun Martin Consulting
Suite 200 - 420 West Hastings Street
Vancouver BC V6B 1L1
604-789-1095
<mailto:smartin at shaunmartinconsulting.com>
smartin at shaunmartinconsulting.com
member CAGBC, ASHRAE
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
RobertGChronic at Eaton.com
Sent: Wednesday, December 15, 2010 2:29 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] equest crashing on chilled water loop
primaryselection
I am having an issue with equest crashing. The error is associated with the
subtype being secondary for the chilled water loop, however, when I switch
it back to primary, I immediately get kicked out of equest. I have
attached the screenshot of equest and the chilled water loop appears to be
nested. I am not sure how this exactly happened, I was attempting to
redefine the chilled water loop. Here is the excerpt from the bdl file. Is
there any way to edit outside of equest interface so I can alleviate the
crashing??
*3099 * "Chilled Water Loop" = CIRCULATION-LOOP
*3100 * TYPE = CHW
*3101 * SUBTYPE = SECONDARY
*3102 * LOOP-DESIGN-DT = 15
*3103 * SIZING-OPTION = PRIMARY
*3104 * PIPE-HEAD = 55
*3105 * PRIMARY-LOOP = "Chilled Water Loop"
*3106 * LOOP-OPERATION = DEMAND
*3107 * DESIGN-COOL-T = 45
*3108 * COOL-SETPT-CTRL = FIXED
*3109 * LOOP-PUMP = "CHW Loop Pump"
*3110 * HEAD-SETPT-CTRL = FIXED
*3111 * HEAD-SETPT = 30
*3112 * ..
*ERROR**********************************************************************
******************
*ERROR*****Chilled Water Loop cannot be specified as a PRIMARY-LOOP due to
incorrect SUBTYPE; valid PRIMARY-LOOP must have a SUBTYPE of
PRIMARY
Thanks!
Robert G. Chronic
Cx Team Leader
Energy Solutions Group
E M C Engineers, Inc.
Eaton's Electrical Services & Systems
408 West University Avenue, Suite 402
Gainesville, FL 32601
tel: +1 352 327-9358 ext. 300
mobile: +1 352 275-7417
fax: +1 352 327-9358
RobertGChronic at eaton.com
<http://www.eaton.com/> www.eaton.com/energysolutions
cid:image001.jpg at 01CB4905.65130300
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101215/53bfdb49/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39998 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101215/53bfdb49/attachment-0001.jpeg>
More information about the Equest-users
mailing list